Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations.....
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?
 
Flow plus return temp

Divide by two

Minus your room temp

Eg

65+50

115/2

57.5

Mins let’s say 18

Gives you a delta t of 39.5

Delta t of 50 you would need your flow and return around 75-65

Which if you have a condensing boiler is bad

TBH I would work off a delta t of 40
 
Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations...
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?
Output of a 50 deg rad is (50/60)^1.3. I , can't work this out in my present location but very easily done on a spreadsheet . You can also and easier look it up in a radiator temperature correction table.
 
Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations...
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?

Slightly misread your post so if the calculation was based @ T65 then the correction factor to run @T50 is 1.41, (65/50)^1.3.
IF it had been based @T60 then the correction factor to run @T50 is 1.27, (60/50)^1.3.
 

Reply to BTU's at delta T65 and T50 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
220
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
214
Hi, I have an old steel water mains pipe (approx 45mm) that I need to connect to a new pehd water mains (25mm). I can't get at it to create a new thread so what's the best way of connecting the two? Cheers, Peter
Replies
2
Views
159
Hi guys. I'm trying to identify a toilet model before ordering a seat for a customer. I went to what used to be a Roca stockist (they no longer are) and one of the guys there reckoned it might be "The Gap". I went to the new stockist and the guy there disagreed it was "The Gap" and that he'd...
Replies
2
Views
113
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
167
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock