Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations...
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?
 
Corgi Direct - PlumbersForums.net Sponsor
This official sponsor may provide discounts for members

ShaunCorbs

S. Mod
Plumber
Gas Engineer
Messages
23,555
Reaction score
6,446
Flow plus return temp

Divide by two

Minus your room temp

Eg

65+50

115/2

57.5

Mins let’s say 18

Gives you a delta t of 39.5

Delta t of 50 you would need your flow and return around 75-65

Which if you have a condensing boiler is bad

TBH I would work off a delta t of 40
 
Messages
374
Reaction score
53
Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations...
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?
Output of a 50 deg rad is (50/60)^1.3. I , can't work this out in my present location but very easily done on a spreadsheet . You can also and easier look it up in a radiator temperature correction table.
 
Messages
374
Reaction score
53
Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations...
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?
Slightly misread your post so if the calculation was based @ T65 then the correction factor to run @T50 is 1.41, (65/50)^1.3.
IF it had been based @T60 then the correction factor to run @T50 is 1.27, (60/50)^1.3.
 

Reply to BTU's at delta T65 and T50 in the Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Test4Less PlumbersForums.net Sponsor
Plumbase - PlumbersForums.net Sponsor
Wetroom Store - PlumbersForums.net Sponsor
uHeat Forum Sponsor - PlumbersForums.net
Power Shower Booster - Official PlumbersForums.net Sponsor
Plumbing Advice - Find Plumbers Jobs
Corgi Direct - Plumbers Forums Sponsor

Test

Top Bottom