Hi
Am unable to find a clear answer to this -

But the water in the cistern with BS 1212 part 2 float valve what is the highest water category that it can be?

Im thinking category 3 has in F and E tank not been able to find anything written in WRAS guidebook.

Can anyone clarify this?
Thanks!
 
Cat 5 if you drill the holes to spec
 
Hi thanks so far but just normal tank with 1212 part 2 valve With out adding extra weir holes into it.

Correct only thing overflow must be sized correctly and terminate to outside

If into stack / waste pipe needs to have an air gap

Weir holes is an AA air gap

IMG_3651.PNG
 
What you planning on doing that's cat 5 risk ?
 
The rainwater harvesting set ups are generally cat 5 due to potential for bacteria etc so yes you would be correct to assume the pigeon faeces would be a cat 5 risk, therefore a suitable back flow prevention set up would be required to provide the appropriate backflow protection against the risk described suirable AB. AA air gaps etc pipe id
 
The use of a BS1212 part 2 float valve does in its self guarantee the air gap it just helps with the amount of water that can be stored & still maintain the air gap.
It always down to the Plumber to drill the holes in the right places to achieve this, air gaps are dependant on the size of the inlet & overflow.
 
Correct only thing overflow must be sized correctly and terminate to outside

If into stack / waste pipe needs to have an air gap

Weir holes is an AA air gap

View attachment 33924
Sorry Shaun but a weir overflow is an AB.
AA is where inlet is above the cistern overspill & free falls into the cistern. Both however are good for Cat 5 & are the only ones that should be used for a rainwater storage if that is what the OP is doing.
ref - WRAS book 6.13
 

Reply to BS 1212 Part 2 Air gap in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
241
Hi guys. I'm trying to identify a toilet model before ordering a seat for a customer. I went to what used to be a Roca stockist (they no longer are) and one of the guys there reckoned it might be "The Gap". I went to the new stockist and the guy there disagreed it was "The Gap" and that he'd...
Replies
2
Views
106
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
141
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock