mr bury

. ideal logic plus c30 , hot water fine boiler wont communicate with reciever honeywell stat sends signal reciever turns on ,will not fire boiler up
 
Assuming Y-plan or S-plan system, boiler receives switched live via the 3 or 2 port heating valve, not directly from the honeywell receiver. So the issue could be with a motorised valve being stuck, or the motor not operating microswitch in valve head.
 

Reply to boiler will not communicate with reciever in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

I have a ideal logic 30 boiler ,the thermostat receiver looks to have died ( no lights on wired receiver ) I believe this need# replacing but in the mean time does anyone know if I can override the thermostat if heating is required please? the handheld thermostat is working it’s the boiler...
Replies
1
Views
806
My heating system comprises an Ideal Logic 12 boiler located downstairs and a Gledhill OV SOL cylinder located upstairs . The problem is that when the Gledhill controls for the “hot water” and “central heading” are turned on the Ideal boiler makes a constant “clicking” noise and tries to start...
Replies
1
Views
473
I've got a non condensing Glowworm Ultimate with gravity tank and hot Water tank in a 4 bed house. 11 radiators 1 double 1400mm length 1 P+ 1400mm length 2 P+ 400mm length 7 singles 400mm 1 mains shower average water pressure Any recommendations on combi boiler and KW? Boiler budget...
Replies
7
Views
489
Ideal Logic Heat 15 System Boiler Hi. Just started to get an F3 Fan Fault on this boiler. On power up there seems to be a quiet thump from somewhere then it goes through the start up sequence. It spends a few seconds on the ‘c’ display before coming up with the F3 error code. Can anyone advise...
Replies
1
Views
930
Deleted member 120897
D
R
Thermostat and Programmer not communicating with Boiler. Both have been replaced. Any ideas? On the Glowworm boiler 18sxi I can use the CH controller to switch on/off the boiler, that works fine. Also upstairs i have a tank, when I switch that on I get hot water. But what else can I check...
Replies
2
Views
596
Deleted member 120897
D
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock