Discuss Boiler pressure problems - pressure high after heating in the Make a suggestion about the forum in general area at PlumbersForums.net

Messages
7
I have a Worcester Greenstar 30i boiler which is about 5 years old and fully serviced. As the days have become colder I decided to put the heating on and noticed that the pressure gauge was sitting at 2 bars cold. I bled a radiator and brought in down to just below 1.5 bars and put the heating on for an hour. Heating worked fine and radiators worked. Once the heating went off, I noticed a few hours later that the pressure gauge had reduced in pressure, but not back to 1.5 bars (sitting half way between 1.5 and 2). I bled a different radiator in the morning and this time reduced pressure to just above 1 bar. I put the heating on and it hit 2 bars while operating. Once it went off and cooled down, again, it hasn't gone back down to 1 bar but is sitting at just below 2.

In summary, I am having to bleed the radiator every time the heating has been on.

Can anyone explain what the issue might be?

Additional info:
A new bathroom was fitted in summer including a towel warmer in place of old radiator.
I have noticed that the keyless filling link doesn't work when pulled - could this contribute to pressure in some way if faulty?

Many thanks
 
I haven't disconnected anything but can't be sure if the plumber who fixed new radiator has. Taken some photos of what I can see which probably isn't that helpful. I have been told by somebody else that I needed to bleed ALL radiators, but I thought 1 would suffice if it reduced pressure.

20210930_150145.jpg
20210930_150159.jpg
 
You should get rid of the air in all rads, you might have to top up the system then as water will replace the released air.
Thank you. I can't top up the system as the refill isn't working :D

Out of curiosity, what difference does draining all of the radiators make rather than just one? If one is enough to reduce pressure, why would bleeding them all stop the issue?
 
Bleeding the system is done to remove trapped air. Air caught in the system can cause air locks which will prevent circulation of water and rads to heat up. Air will also cause corrosion. ALL air must be removed.

As I said above I suspect the PHX
 
All rads need to be bled. Any idea what your static cold main pressure is? I'm thinking the HW plate heat exchanger has split.
No idea on the main pressure. Got a feeling this is a problem I can't fix myself as I am totally out of my depth.

I can bleed all the radiators, but can't refill boiler if the refill isn't working.

Thanks
 
You are not allowed to touch your boiler and I commend you for acknowledging that and that you're out of your depth. If the filling valve isn't working then no you can't top the pressure up.
If you were to drain all of the water out of the system you would then see if the plate had failed as the system would start filling again and stabilising at whatever the cold mains static pressure is, or the discharge valve setting, whichever is lower. However if it wasn't the plate then you can't refil the system and would have no heating or hot water.
I suggest getting a gas engineer out ASAP.
 
No idea on the main pressure. Got a feeling this is a problem I can't fix myself as I am totally out of my depth.

I can bleed all the radiators, but can't refill boiler if the refill isn't working.

Thanks

When I am bleeding all, am I just doing it until the air is out or completely draining system to stop the issue. All radiators are hot, top to bottom before I do it.
 
You are not allowed to touch your boiler and I commend you for acknowledging that and that you're out of your depth. If the filling valve isn't working then no you can't top the pressure up.
If you were to drain all of the water out of the system you would then see if the plate had failed as the system would start filling again and stabilising at whatever the cold mains static pressure is, or the discharge valve setting, whichever is lower. However if it wasn't the plate then you can't refil the system and would have no heating or hot water.
I suggest getting a gas engineer out ASAP.
Thank you for trying to help anyway! I have booked one. Coming tomorrow.
 

Reply to Boiler pressure problems - pressure high after heating in the Make a suggestion about the forum in general area at PlumbersForums.net