2
Hi

I have a 20 year old Gledhill Boiler Mate 2 thermal store (BM2). It's been working with a Potterton 24kW Pro Max boiler for many years. It was recently inspected and all working well.

The Potterton boiler died and was replaced with a Vaillant 32kW open vent heat only boiler, and the whole system was given a chemical flush. The following problems occurred that evening and getting worse daily:

1. The new boiler went into fault mode f.83 (sensors detecting insufficient temperature increases, after the burner has been lit.)
2. The BM2 developed glugging, flushing, dumping, crashing and banging noises. These were intermittent, but appeared cyclical. They do not happen constantly, they happen mostly between midnight and 6am (notably when the outside temperature is at its lowest). This is definitely a new thing since the boiler was changed.

The boiler is then either reset manually, or after a while automatically. The thermal store is sometimes cold as a result, and I wonder if recovering from cold to normal storage temperatures triggers the problem. However, I've read many articles that indicate this is likely to be a blockage in the cold fill pipe which will need a new bypass installing.

I'm looking for thoughts on the following please:
1. If the cold fill pipe is blocked would the symptoms be apparent all the time, or would there be periods of normal operation (we're getting a mix of both).
2. If it is related to air in the system would it lead to these BM2 problems. If so, wouldn't that be apparent whenever the heating is on?
3. If it is a BM2 pump fault wouldn't that be apparent whenever the heating is on?
4. Other thoughts on why this might happen mostly at night but work better during the day.

Just for clarity, the boiler does go into f.83 frequently during the day. I just don't hear the BM2 noises as oftern.

Many thanks to anyone who can offer knowledgeable info. I'm am untrained homewoner just trying to figure it all out.
 

Reply to boiler mate 2 banging noises in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
222
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
300
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
227
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
354
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock