14
Hi all.

Would really appreciate some advice if possible, I have a valiant combi boiler and over the last couple of years it randomly seems to lose pressure,it will be fine today and then i'll go to put the heating or hot water on and nothing, i re-pressurised the boiler and all works fine, it can be run for months with no issues then it will happen again.

I have been through all radiators,valves, and trv's and there are no leaks which are visable, i had an engineer in about a year ago and he opened up the boiler pumped some air into the expansion vessel i think and everything seemed fine until it started doing it again over the last week, he said it was a common fault with these boilers.

My question is does this sound like something that the expansion vessel would do if faulty? i really dont want to start lifting the floor up looking for leaks so before i do i would like to hear what you guys think.

Thank you in advance
 
1. If the expansion vessel is faulty, then, when the water is heated, the pressure will rise. If it reaches 3 bar, then the pressure relief valve will operate and dump water to outside. When the boiler cools it has no automatic way of replacing the dump water, so the pressure falls.
2. Check the point (normally outside) where the over pressure water is released. Usually a copper pipe "turned over" with fittings to point back against the wall. If there are signs of dripping, it is an expansion vessel / pressure relief valve issue. If no signs of dripping, tie a plastic bag over the end, and, the next time there is a problem, see if there is water in it.
 
1. If the expansion vessel is faulty, then, when the water is heated, the pressure will rise. If it reaches 3 bar, then the pressure relief valve will operate and dump water to outside. When the boiler cools it has no automatic way of replacing the dump water, so the pressure falls.
2. Check the point (normally outside) where the over pressure water is released. Usually a copper pipe "turned over" with fittings to point back against the wall. If there are signs of dripping, it is an expansion vessel / pressure relief valve issue. If no signs of dripping, tie a plastic bag over the end, and, the next time there is a problem, see if there is water in it.
Thanks for the input, i will give that a try and see what happens, i know where the pipe is so i'll give it a try after and see if any water comes out.
 
Just a quick update, so went to the boiler last night and there was no pressure so i topped it up and done as suggested and put a carrier bag around the copper outlet pipe and sealed it up. This morning tried to use the hot water and there was none so i knew that the pressure had dropped again, when i went and checked the bag there was a cup full of water inside the bag, so would that confirm that it is an expansion vessel/ Pressure relief valve issue?

Thanks in advance =)
 
Yep time for a gas safe engy I’m afraid
 
Just a quick update, so went to the boiler last night and there was no pressure so i topped it up and done as suggested and put a carrier bag around the copper outlet pipe and sealed it up. This morning tried to use the hot water and there was none so i knew that the pressure had dropped again, when i went and checked the bag there was a cup full of water inside the bag, so would that confirm that it is an expansion vessel/ Pressure relief valve issue?

Thanks in advance =)
You may find it cheaper to put an external expansion vessel in rather than go for a bespoke one
That’s certainly the problem the difference between 0 and 2 bar on a domestic system might only be
2 litre...the rest is in the exp. pipe. Chking
 

Reply to Boiler losing pressure in the USA area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
230
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
301
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
213
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
253
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
377
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock