Hi all,

I am not sure whether anyone ever saw this issue....

My Worcester Bosch boiler was installed last year August, since then I found the boiler green light (burner light) will be off after HW is satisfied(supposed to be), but after 2 mins it will be back on again! For 2mins of firing, the green light will be off, then after 2mins it will be back on! Throughout this repetitive process, the blue light (power light) is on all the time---i.e zone valve for HW is open all the time.

I called cylinder manufactory Joule to come to check, they extended the copper temperature sensor inside the cylinder temperature box and changed new cable---now the boiler blue light will be off i.e. zone valve will be closed after HW is satisfied (before zone valve never closed, blue light always on), BUT, I find the green light will still be off first, then after 1 or 2mins, it will be back on! Then after firing 1min or 2mins, either it will be off or Blue light off---once blue light off (means zone valve closed), the green light will be off.

To put simply, my issue is: why green light will be off for 1 or 2mins, then back on? Then go off again, then back on, until blue light off, then green light will be off accordingly.

What I know for boiler lights operation is, once zone valve opened, the boiler blue light (power light) will be on first, then green light (burner light) on; When zone valve closed, blue light will be off then green light off immediately----Green light should not off then back on, then off then on.

Anyone notice your boiler has this issue? Or know what could be wrong?

Thanks!
 

Attachments

  • boiler light.png
    boiler light.png
    421.9 KB · Views: 6
  • boiler lights.png
    boiler lights.png
    298.9 KB · Views: 3
For S-plan type systems, which is what I think you probably have, the boiler flow temperature needs to be at least 5°C above the set-point on the thermostat that controls the domestic hot water zone valve. The minimum DHW temperature I recommend (for systems that have a single constant flow temperature set-point) is 60°C. So, if your hot water is stored at 60°C, the flow temperature needs to be 65°C or greater.

So, I'd start by measuring the temperature of the DHW to see if there is scope for reducing it. if not, try turning the temperature knob on your boiler up by 5°C (about one division), which should have the desired effect.
 
For S-plan type systems, which is what I think you probably have, the boiler flow temperature needs to be at least 5°C above the set-point on the thermostat that controls the domestic hot water zone valve. The minimum DHW temperature I recommend (for systems that have a single constant flow temperature set-point) is 60°C. So, if your hot water is stored at 60°C, the flow temperature needs to be 65°C or greater.

So, I'd start by measuring the temperature of the DHW to see if there is scope for reducing it. if not, try turning the temperature knob on your boiler up by 5°C (about one division), which should have the desired effect.
Thanks for your suggestion!
Actually your suggestion did make effect! I didn't put more details in my original post, what you mentioned I had done all those. The HW temperature in my house is about 60°C, before my boiler temperature was around 74°C----at the time the boiler green light always off/on alternatively & blue light never off, so the boiler was operating all the time.
Now, as I turned the boiler temperature up to around 80°C now, the blue light will be off now (zone valve closed), but green light still back on for 1 or 2 minutes then off before blue light off----previously green light back on and off all the time.
 
The HW temperature in my house is about 60°C, before my boiler temperature was around 74°C
A 14°C difference should be more than enough for the system to behave properly. Increasing the difference to 20°C is helping by transferring heat more rapidly but is not getting to the root of the problem.

The problem, heat not being removed from the boiler faster enough, remains so the next thing to check is the circulation rate. This could be low due to the zone valve not opening fully, a balancing valve being too restrictive, a clogged filter, weak pump, etc.
 
A 14°C difference should be more than enough for the system to behave properly. Increasing the difference to 20°C is helping by transferring heat more rapidly but is not getting to the root of the problem.

The problem, heat not being removed from the boiler faster enough, remains so the next thing to check is the circulation rate. This could be low due to the zone valve not opening fully, a balancing valve being too restrictive, a clogged filter, weak pump, etc.
Thanks again!
"The problem, heat not being removed from the boiler faster enough, remains so the next thing to check is the circulation rate. This could be low due to the zone valve not opening fully, a balancing valve being too restrictive, a clogged filter, weak pump, etc."====all these could be the reason the boiler green light off first then back on, then off, till blue light off?
 

Reply to Boiler green light off then back on? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi all Noticed bad smell in my drain out side put my hand down and it unclogged it for now however I checked my sewer drain and after flushing my toilet a good few times nothing is going to the sewer so don't know is there a blockage or what way it works many thanks and advice would be grateful
Replies
3
Views
417
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
151
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
253
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
130
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock