Hi Guys

I had UFH added to my extension, my system was a Baxi 30he with CH and unvented cylinder.

The UFH has never really worked correctly first of all I noticed they had install the flow and return the wrong side of the circulation pump which I rectified myself as they have disappeared on me. The UFH now works but I have noticed an issue that if the CH is not running the boiler cuts out if the UFH is calling for heat. If the CH is running then the UFH runs fine, I’ve been searching online for diagrams


Do I need an auto bypass valve on the flow and return after the circulation pump ? At the moment the circulation pump is in the loft and the boiler on the ground floor about 8m away and all my rads have TRV fitted?
 
What temperature is the boiler set to, the UFH manifold (flow) temp and what is the UFH return temperature, if known?.
Also boiler make/model.
Edit: See its a Baxi 30he
 
Last edited:
You will find the ufh heat load is less than the boiler min load so it will cycle two options use a buffer or llh/ccts
 
That boiler has a minimum output of 11.9kw so will definitely spend a lot of time cycling with the UFH only on.
A LLH or some form of bypass won't prevent this but will reduce the dT across the boiler, with no by pass and assuming boiler flow temp of 70c with UFH manifold of 45C/35C then the boiler dT is 35C, a boiler flow temp of 65C will give a dT of 30C and 60 will give a dT of 25C, the boiler may not have a dT trip.
 

Reply to Auto bypass required ? in the The Welcome Wagon :) area at PlumbersForums.net

Similar plumbing topics

Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
218
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
218
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
346
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
289
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
195
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock