I am a DIY'er and I need to replace the 3-port valve of my bungalow. I am aware I could bung the F&E but I don't really want to chance this approach with the risk of water going everywhere, but I'd also rather not FULLY drain the heating system.

Possibiy a dumb question but the 3-port valve is quite high up, so I was wondering since all the radas are on the ground floor whether there was any way I might half drain the heating system so the water level is lower than the valve but the rads are still full. Is that even a thing?

Alternatively, is there anyway I can isolate the 3-port valve using the valves either side of the pump?

Here's a picture of the setup etc if it helps.

20220926_175534.jpg


Really appreciate any advice.
 
Do you actually need to replace the valve? If you so, then yes, just drain to a level below the 3 port.
Yes I believe I need to replace the valve, having removed the actuator head, the valve always sends hot water to both HW and heating regardless of what position I move the "bolt" on top of the 3-port valve.

Any tips on how I can determine I've drained the system enough such that the level is below the 3 port?
 
@Last Plumber thank you.


Also, all the 3-port replacement YTs I've watched explain how to bung or drain the heating system but there's NOTHING
MENTIONED about draining or plugging the hot water. Do I need to do anything there or does that part of the system naturally hold its water because of a vacuum? Whats going to happen to all the water in the pipe that leaves the B part of the valve?
 
@Last Plumber thank you.


Also, all the 3-port replacement YTs I've watched explain how to bung or drain the heating system but there's NOTHING
MENTIONED about draining or plugging the hot water. Do I need to do anything there or does that part of the system naturally hold its water because of a vacuum? Whats going to happen to all the water in the pipe that leaves the B part of the valve?
The water in the coil (inside the cylinder) and the heating system are the same system water in your case (primary water).

So long as the coil is intact, there won't be any water from anywhere else.
 
@Last Plumber , aha, yes of course. Thanks so much you've been really helpful.

I have now successfully installed the new valve and attempted to refill the system. HOWEVER, when I turn on any combination of HW or heating none of the three pipes around the 3-port valve are heating up. The boiler seems to fire briefly but then go off.

What might cause this issue, could it be an air-lock?

I've tried continously bleeding from 1. the cylinder bleed valve, 2. the magnaclean bleed valve & 3. the pump (as per pic below). 1 & 2 work good HOWEVER I can remove the metal (bleed) plug from the pump entirely and no water comes out.

Any suggestions greatly appreciated. 😬

20220926_175553.jpg
 
Check the water level in the feed and expansion cistern in the loft.
Thanks, I'd already ensured the tank was full in the loft when refilling.

Anyway, I think I've got it working now. I found another couple of bleed valves in the loft where the pipes go to and from the boiler. Only a little air came out of these, so not sure that was it, but having continued bleeding all the valves the system didn't eventually seem to start pumping hot water.

Hopefully its sorted now. Really appreciate all the prompt and helpful input. 🙇🏼
 
Air locked air is a pain sometimes just need to keep bleeding stuff etc
 

Reply to Advice on draining system of bungalow to replace 3-port valve in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
221
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
304
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
384
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
230
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
212
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock