Can anyone tell me if its actually a reg or just good practice that a switched socket outlet (as well as a switched spur) MUST be fitted next to boilers in lofts so when service engineer visits there is somewhere to plug in equipment should he need it ?

I have always done it but wasnt sure if it was actually a regulation
 
No requirement in regs for a socket.
I wouldn't put one in, apart from my core drill and breaker everything I have is lithium powered!
 
Not sure there are any actual gas regulations that for boilers in loft, although I'm happy to be proven wrong.
As far as I know it is just general health and safety for a permanent ladder, correct lighting, boarding and a rail around the hatch. Most manufacturers will require this for warranty to be honoured.
Electrical isolation on a fuse spur is appropriate for any location. However it is a nice addition if there is a socket as well.
I can't see any reason for additional gas and electric isolation on the landing. Only one thing I often consider is a filling loop and pressure gauge in the airing cupboard or such like for easy top ups.
 

Regulations​

BPEC CEN1 Guidance regarding roof installation of a gas boiler is:

  • Flooring provided to the boiler for service access
  • The boiler has to be mounted on a wall capable of withstanding weight.
  • Loft to be accessible with retractable ladder
  • Must have fixed lighting in place
  • The roof space exit must be protected with a guard rail
  • Gas, water, and electrical isolation points should be provided outside of the roof space so the boiler
    can be isolated without gaining access to roof space.
 
According to BS 6798:2014
Guard rail is essentially a reccomendation in commentary under reg 7.3.8.1c
I don't read it as a requirement!
Isolation points has been grabbed from somewhere else (or made up by author) and as far as I can tell is not in the regs altho you would have ECV, stoptap and consumer unit outside the loft by default?
 
IIRC in the electrical regs you just need double pole isolation, so a plug or DP fused spur will suffice

as for being able to isolate the boiler without going in the loft is a new one on me.
 

Regulations​

BPEC CEN1 Guidance regarding roof installation of a gas boiler is:

  • Flooring provided to the boiler for service access
  • The boiler has to be mounted on a wall capable of withstanding weight.
  • Loft to be accessible with retractable ladder
  • Must have fixed lighting in place
  • The roof space exit must be protected with a guard rail
  • Gas, water, and electrical isolation points should be provided outside of the roof space so the boiler
    can be isolated without gaining

Regulations​

BPEC CEN1 Guidance regarding roof installation of a gas boiler is:

  • Flooring provided to the boiler for service access
  • The boiler has to be mounted on a wall capable of withstanding weight.
  • Loft to be accessible with retractable ladder
  • Must have fixed lighting in place
  • The roof space exit must be protected with a guard rail
  • Gas, water, and electrical isolation points should be provided outside of the roof space so the boiler
    can be isolated without gaining access to roof space.
Thanks for posting that, I wasn't aware of the requirement for additional isolation, but the rest I guess is common sense. I have also seen drain points added into the condensate pipework which is a nice touch if you have to drain the boiler.
 

Regulations​

BPEC CEN1 Guidance regarding roof installation of a gas boiler is:

  • Flooring provided to the boiler for service access
  • The boiler has to be mounted on a wall capable of withstanding weight.
  • Loft to be accessible with retractable ladder
  • Must have fixed lighting in place
  • The roof space exit must be protected with a guard rail
  • Gas, water, and electrical isolation points should be provided outside of the roof space so the boiler
    can be isolated without gaining access to roof space.

when they say “guidance” is this a must have and if so who’s responsibility is it to check this is in place?

as a spark I’ve not come across this requirement before but will now bear it in mind as I don’t think it’s mentioned in our regs

that said the muppets are creating a web of cross references which makes this stuff quite difficult to keep up with
 
It’s one of this practical things fused spur next to the boiler is more than good enough

guess you could class the mcb/rcbo as an isolation point if there fussy

as for a socket it’s a handy thing to have and if designing a new install would recommend one there as it wouldn’t cost much to do it at the time or have the boiler on it’s own circuit rated for a socket then spur off the socket wtc
 

Reply to Additional electrical socket for boiler in loft in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

My Grant combi oil boiler is giving me quite a headache at the moment. When I returned home last Friday I'd no heating or hot water. An engineer called the next day and diagnosed a faulty pressure switch. This was changed and everything seemed ok. However then the boiler began to lose pressure...
Replies
3
Views
538
Can anyone help, please? I'm looking for a heating system circulation pump for a domestic install, with 3 speeds, where the speed can be toggled electrically as well as via a push switch on the pump body. I'm using this pump with a wood boiler stove, where I want to run the pump at its slowest...
Replies
6
Views
966
A
Previously had a WB Greenstar R28 HE System boiler with 4 pipes and vented (gravity fed) cylinder. No valves or pumps outside of the boiler. Worked fine for 20 years. Decided to change to Viessmann 050-W System boiler when WB failed but keep the same set up with cylinder. Gas Safe installer I...
Replies
1
Views
854
Deleted member 120897
D
P
I currently live in a 4 bed end of terrace victorian house, with 11 radiators and two towel rails. Currently have installed a 6kw potterton gold electric boiler, which heats a hot water cylinder and provides heating to the radiators. My electricity usage is extremely high and killing me...
Replies
15
Views
2K
Hi all, Hope you’re all doing well. I had a new bathroom installed recently which involved new piping, and also capping off some redundant pipes. Since then, my boiler (pretty new Vaillant combi) turns on when I turn the cold water on. I’ve done some reading and it seems like the problem is...
Replies
3
Views
714
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock