DHW consumption - A lot - if you've ever seen the impact a shotgun competition has on a clubhouse, 72 sweaty golfers descending on the bar and clubhouse over a matter of 40 minutes. Hence they have 9 showers in the mens' changing rooms.
600 litres of DHW with rapid reheat should be sufficient.

Client has decided (correctly) that AS heat pumps will never work in this situation. So we're looking at reconfiguring the Cylinders - the DHW secondary connections are also plumbed the wrong way round, and in series not parallel so big c**k up there, and no reverse return / Tichelmann on the primaries.

Cylinders can (probably) be reused, system needs complete re-plumbing, new / proper heating controls and cascaded gas boilers, plus need to look at possibly pumped DHW to the showers, even though it is currently unvented as supply to them is undersized. (Single 22mm)
Anyone fancy a punt -- we don't do gas !
 
Lock the shower block doors and invest in a happy hour at the bar? Probably the cheapest solution!
 
Status
Not open for further replies.

Reply to ACV Cylinders - back to front?? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock