Jennie

Gas Engineer
Messages
283
Hi all,
Just getting my head in a twist regarding the 3-tee rule (last tee on the return pipe should be hot water).
I have a customer with an unvented installation, with two 2-port valves for CH and HW. He's built an extension, and wants to add a new circuit of radiators to the system. The new leg of rad pipes would cut in just under the boiler, with the new rad pipes becoming the last tee on the return (instead of the hot water), and also cutting in after the bypass valve below the boiler. The flow would cut in just after the central heating 2-port valve.
Could breaking the 3-tee rule lead to reverse circulation (when hot water is on, the new radiators get hot)? Surely a closed 2-port valve should stop any circulation, or could the circulation occur up/down within that return pipe? Or if it's a problem, could i put a non-return valve on?
My preferred option is to follow good piping design, and cut the new rad pipes in further down the pipework, before the HW return and away from the bypass. Though the pipework won't be as convenient, and I'd need to drain down the system.
He's particularly keen to put the connections under the boiler, as I'm due to change a faulty zone valve using a pipe freezing kit, (to save draining down a big property). Hence he's keen to fit the new pipes in at the same time, in the frozen section, and get everything up and running quickly.
Advice would be much appreciated.
Thanks
Jennie
 
I think the concern in your case is parasitical circulation within a single pipe when in DHW-only mode. To be honest, I think there is a risk of the same happening to the cylinder when a system that complies with the 3 tees rule is in CH-only mode, but it's less of a problem which is probably why we generally ignore it.

I suppose non-return valves would prevent this happening. Perhaps an anti-gravity loop would also work with fewer potential downsides?
 
How far is the cylinder from the boiler, or where do the returns meet? Is it a sealed primary system?
 
The 2 port valve won't stop the reverse circulation (as the water doesnt flow through it when this occurs).

The return water from the HW cylinder may go back up the return pipe for the CH (as it is the last tee). It will then flow in reverse through the radiator flow pipe to the next radiator and then back down the return pipe of the second radiator, before returning to the boiler.

There was a brilliant diagram posted on this forum many years ago, but I cant find a link to it right now.
 
The 2 port valve won't stop the reverse circulation (as the water doesnt flow through it when this occurs).

The return water from the HW cylinder may go back up the return pipe for the CH (as it is the last tee). It will then flow in reverse through the radiator flow pipe to the next radiator and then back down the return pipe of the second radiator, before returning to the boiler.

There was a brilliant diagram posted on this forum many years ago, but I cant find a link to it right now.

Thanks so much. It finally makes sense. :)
 

Reply to 3-tee rule on unvented cylinder in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, I'm in my new build 2 years and the shower pump has died. I have an air to water unit downstairs is in the utility which I've been told is unvented and pressurised. The cold water feed into this cylinder is from the attic tank, not the mains as I turned off the mains stopcock to see if hot...
Replies
6
Views
160
Good evening, I'd like your opinion on something that is worrying me please: my landlady's plumber replaced the bottom/night element of my 20-year-old unvented cylinder (an Ariston Classico HE STD 150) 5 days ago and I hadn't noticed that it was leaking. He fixed the leak today but now the...
Replies
2
Views
432
Hi There was no shut off valve on the tank feed to the hot water cylinder, and I needed to move a couple of hot water pipes, so I shut off the mains water, turned boiler off (Remeha avanta) and opened the hot kitchen tap to drain the cylinder. After doing the work etc, Everything up and...
Replies
4
Views
212
Hi all. As the title says, I have a problem with an unvented cylinder I had installed last year where the first time I turn a hot tap on after the cylinder has been heated I get what sounds like a vibration. It generally starts about 1s after I open the tap and lasts for about 1.5s. I've...
Replies
27
Views
2K
Hi, I’m having issues with cold water to multiple outlets. Taps, showers, toilets cold water is fine at the kitchen sink. The hot water system is a Glenhill unvented cylinder. Hot water is fine at all outlets. I assumed the cold outlets not working were from the balanced cold from the...
Replies
18
Views
2K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock