Hi
Overflow suddenly spouting out luke warm water to outside of house, checked on down pipe in photo leads exterior overflow, could put finger spout when overflowing and its luke warm water.

Why is it overflowing? Lot of water coming out.

Photo attached of side of tank to show above.

What is wrong???
 

Attachments

  • IMG_1771.jpeg
    IMG_1771.jpeg
    453 KB · Views: 12
Over time the cylinder can loose its air bubble there is a floating baffle inside your cylinder the air gap needs resetting, turn off the mains cold water supply to the cylinder open up 2 hot water taps and leave them open go back to the cylinder,
The black knob on the pressure relief is spring loaded turn it clockwise until you feel a click hold it in that position hot water should drain from your taps and copper pipework realeasing any built up pressure , once the water stops it's simply a case of shutting the relief valve close one hot tap, then slowly turn the cold supply back on refilling the cylinder this will reset the air gap water will vent from the hot tap let it run for a minute or so then switch off , Try this and see if it cures your problem. Kop
 

Reply to Hot water leaking at overflow in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi all, Just recently noticed the overflow has started pouring water out, there are three tanks in the loft and I'm quite sure this is from the heating. We have two boilers, one for water and one for the heating, it's an 8 bed Victorian house (bed and breakfast) I went into the loft to see what...
Replies
8
Views
845
Hi all I have a problem with my hot water header tank getting warm water into it from the bottom of the header tank (not the hooked overflow/expansion pipe. Hence the header tank then reaches the overflow level and the overflow trickles out. I have changed the ball valve washers thinking it was...
Replies
1
Views
647
Hi, We have a large Heatrea Sadia unvented hot water tank, not sure of the size in liters but its about 1600mm tall. The tank is around 3 years old now and was amazing when it was first installed. Around a year ago we had a problem with water dripping from the overflow pipe outside and we ended...
Replies
0
Views
381
Looking for any ideas to help. I've a Heatrae Sadia Hot Water tank, heated through Oil fired boiler (working fine). A week ago I reset the air gap as I was having dripping from the pressure relief valve. Since then I've lost a lot of pressure from the hot water feed to my shower. The rest of...
Replies
8
Views
262
Heĺlo I have a water leak under bathroom floor tiles. It is on the hot water feed to the tap. I noticed the tiles leading to sink warm last few days. Now my radiators are not heating up because the hot water must be getting diverted to the tap. What are my options? Can I get house insurance...
Replies
11
Views
654
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock