Messages
113
My daughter has just had a new boiler, her system is radiators to upper floors and underfloor to all of ground floor. Despite the valve serving the underfloor being turned up to a high temperature and the pipe leading to the pump being very hot the flow and return pipes on the manifold are only luke warm. The valve is on 60 or 65 but the temperature on the dial after the pump is only 30 degrees. I enclose a photo with the flow and return marked in yellow and the hot pipe leading to the pump marked in blue. The pump sounds as if it is working ok. In addition I can’t see how the flow on each circuit can be adjusted as the flow indicators do not look like they can be adjusted but there has to be a way.
Any advice would be much appreciated
 

Attachments

  • A305CFD6-6FB5-430E-8149-4B53A02AF9E8.jpeg
    A305CFD6-6FB5-430E-8149-4B53A02AF9E8.jpeg
    472.1 KB · Views: 21
  • CFA62C96-8459-4FCC-A68E-71B3923A5E1E.jpeg
    CFA62C96-8459-4FCC-A68E-71B3923A5E1E.jpeg
    360.3 KB · Views: 20
Also you shouldn’t have the ufh system running at 60 dc what was it designed at ?

There’s flow going through them and adjusting them won’t fix the problem as there pumping / flowing best to stop adjusting things and find what the actual problem is before you break something
 
Also you shouldn’t have the ufh system running at 60 dc what was it designed at ?

There’s flow going through them and adjusting them won’t fix the problem as there pumping / flowing best to stop adjusting things and find what the actual problem is before you break something
I haven’t done anything. The engineer that installed the new boiler said to turn up to 60 for a while as the underfloor wasn’t getting very warm so my daughter did what he said. I haven’t adjusted anything, my question about how to adjust the flow was just out of interest, I just try to advise/ help when I can but I will not be touching it, I will leave that to the experts.
 
I haven’t done anything. The engineer that installed the new boiler said to turn up to 60 for a while as the underfloor wasn’t getting very warm so my daughter did what he said. I haven’t adjusted anything, my question about how to adjust the flow was just out of interest, I just try to advise/ help when I can but I will not be touching it, I will leave that to the experts.
 
I haven’t done anything. The engineer that installed the new boiler said to turn up to 60 for a while as the underfloor wasn’t getting very warm so my daughter did what he said. I haven’t adjusted anything, my question about how to adjust the flow was just out of interest, I just try to advise/ help when I can but I will not be touching it, I will leave that to the experts.

Well that’s bad advice from him high temp can cause the floor to crack / warp / do some decent damage did he flush the loops as he’s drained down ?

The flow is set to spec so should need adjusting
 
Did the system work with the old boiler? Can you upload a picture of the new boiler with surrounding pipework.
Yes it did work with the old boiler which was a Remeha 45KW . The heating was off for nearly two weeks while getting a new one installed was all sorted. The enclosed photo is of the low loss header below the old boiler, that is still there. The new boiler is Worcester Bosch regular boiler, sorry no photo as daughter lives on other side of Leeds.
 

Attachments

  • 7A3B79AD-5693-498D-B6DB-0A4614B6FE36.jpeg
    7A3B79AD-5693-498D-B6DB-0A4614B6FE36.jpeg
    305.2 KB · Views: 13
Well that’s bad advice from him high temp can cause the floor to crack / warp / do some decent damage did he flush the loops as he’s drained down ?

The flow is set to spec so should need adjusting
I will tell her to turn it down. You say the flow is set to spec so should need adjusting, did you mean to say shouldn’t need adjusting ?
 
Could be air locked. Need mains on and flush through each loop.
Yes, it could be. The problem they have is the contract with Corgi who kindly replaced the boiler and separate pump does not cover the underfloor heating. The engineer who replaced the boiler is just trying to get it running like before but I doubt that he would flush through each loop.
How are the flow rates on each loop adjusted ? as the flow indicators do not look as if they have any adjustment. I have seen a few videos on YouTube where they simply adjust the flow indicator but that doesn’t look possible on their system
 
I’ve been to my daughter’s again this morning and taken a few more pics and felt the temperature of the flow and return on the underfloor heating manifold. The 15 mm supply pipe is very hot until it joins the valve arrowed yellow which links with the return flow on the manifold after that it is only lukewarm and the temperature gauge shows around 28 degrees. I am not a heating engineer but is this a mixing valve and would turning the nut increase the ratio of new hot water to the return water from the manifold ? Her floors are definitely warmer but not as warm as they should be which makes sense if the water flowing from the manifold is not hot enough.
 

Attachments

  • CD5C035E-21EB-4F28-8569-D798FA30E78D.jpeg
    CD5C035E-21EB-4F28-8569-D798FA30E78D.jpeg
    486.6 KB · Views: 13
  • 9974A67C-9A65-4FCD-8672-82A09E081AE5.jpeg
    9974A67C-9A65-4FCD-8672-82A09E081AE5.jpeg
    493.9 KB · Views: 12
Yes it did work with the old boiler which was a Remeha 45KW . The heating was off for nearly two weeks while getting a new one installed was all sorted. The enclosed photo is of the low loss header below the old boiler, that is still there. The new boiler is Worcester Bosch regular boiler, sorry no photo as daughter lives on other side of Leeds.
More pics of the installation after new boiler. I have posted separately asking if the valve arrowed yellow is a mixing valve and if adjusting this would increase the temperature of the water flowing through the manifold. Is it just a matter of turning the nut and which way would make it hotter?26810B00-B651-4BBC-A787-8A44E38A605F.jpeg822CD4F0-5E5D-4D29-BFA9-2A3600BF43AE.jpegA90EE17C-DFDE-436D-A9FC-11081AE68E53.jpeg72E19741-C000-46E8-9AC7-E40A8E214D48.jpeg24384940-3097-483C-916C-BDF76BC9DAC4.jpeg
 
Stop mucking about , get the installer back- or another competent plumber who knows what they’re looking at.
I agree, I am not mucking about just trying to give a bit of advice but not touching anything. It is not entirely straightforward as Corgi have replaced the boiler as the original Remeha was condemned and it was only eight years old but they don’t cover underfloor heating systems. The new installer has got the system running with new Worcester Bosch boiler but the underfloor is not as warm as it should be, he is trying to work out why but strictly speaking they are not responsible for the underfloor part. They may have to get somebody else back if he has no luck tomorrow
 
That’s what I mean, you need someone who knows what they are looking at not someone who can just chuck a boiler on the wall - if it works fine, if it doesn’t they haven’t got a clue.
 
More pics of the installation after new boiler. I have posted separately asking if the valve arrowed yellow is a mixing valve and if adjusting this would increase the temperature of the water flowing through the manifold. Is it just a matter of turning the nut and which way would make it hotter?View attachment 81264View attachment 81265View attachment 81266View attachment 81267View attachment 81268
Can you take the 4 LLH temperatures with a thermal gun or the like you may be able to get the boiler flow and return temps from the boiler itself, also any displayed tempsfrom the UFH manifolds, takeany temps with rads only on, UFH only on and with both RADS&UFH on.
 
Can you take the 4 LLH temperatures with a thermal gun or the like you may be able to get the boiler flow and return temps from the boiler itself, also any displayed tempsfrom the UFH manifolds, takeany temps with rads only on, UFH only on and with both RADS&UFH on.
The boiler flow and returns are fine, all the radiators are fine. The flow pipe from the boiler to the UFH is fine but after it links with the return from the UFH it is only lukewarm, this then goes through the pump and back into the flow manifold to the UFH. It seems to me that there is too much of the return water and not enough of the new hot flow from the boiler when they are mixed but how can that be adjusted. The new boiler installer simply turned the thermostatic valve up to 60 degrees but that didn’t make any difference, still lukewarm water circulating through the UFH.
 
If you had a 5kw UFH demand with flow/return of 45C/37C from a boiler flow temp of 65C then a hot flow of 3.59LPM at 65C mixed with 5.36LPM of UFH return water at 37C is required to give a UFH flow of 8.95LPM with a dT of 8C &5kw.
You may require separate pumps on rads and UFH if both fed from the LLH.
Does the UFH perform OK on its own?
 
Can you take the 4 LLH temperatures with a thermal gun or the like you may be able to get the boiler flow and return temps from the boiler itself, also any displayed tempsfrom the UFH manifolds, takeany temps with rads only on, UFH only on and with both RADS&UFH on.
If you had a 5kw UFH demand with flow/return of 45C/37C from a boiler flow temp of 65C then a hot flow of 3.59LPM at 65C mixed with 5.36LPM of UFH return water at 37C is required to give a UFH flow of 8.95LPM with a dT of 8C &5kw.
You may require separate pumps on rads and UFH if both fed from the LLH.
Does the UFH perform OK on its own?
There are separate pumps to rads, UFH and also to the hot water. The UFH doesn’t perform Ok on its own it isn’t terrible it just doesn’t get very warm. As I said before the supply to it is hot but just not hot enough once it mixes with the return flow.
 
Assuming the UFH TMV is working correctly it still requires ~ 10C/15C differential to operate properly so possibly the LLH secondary flow is excessively higher than the primary flow which means the UFH return will just short circuit the excess to the flow side.
 
Assuming the UFH TMV is working correctly it still requires ~ 10C/15C differential to operate properly so possibly the LLH secondary flow is excessively higher than the primary flow which means the UFH return will just short circuit the excess to the flow side.
Good point. My daughter rang me yesterday and said that following the latest visit from the boiler installer to tidy up some electrics the UFH was now working perfectly. Unfortunately she wasn’t there at the time but is texting him to see if he had done anything to the UFH circuit as he had previously said he didn’t know why it wasn’t hot enough. I will post if I find anything out. Thanks for your advice.
 

Reply to Underfloor heating not getting hot enough in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
132
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
226
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...