Happy Christmas everyone,

We’ve just had a new Gledhill Stainless Lite indirect unvented cylinder installed by Dyno. It is making an alarmingly loud popping noises when the hot water is being used, not always but very very often.

Mentally to me, it seems like the inner casing of the cylinder is flexing in and out (just like a plastic water bottle under a pressure change).

I have read that these are thin cylinders (hence the lite) and many have reported issues, even after a replacement.

Those of you experts out there who are familiar with this cylinder and it’s issues, is my best course of action to get Dyno to replace with another brand/model, rather than go with a replacement of the same brand/model?

Dyno have requested Gledhill to come on site, but I have read some posts saying the problem reappears after replacement. The visit will now take place in the new year, but I want to be prepared and not be fobbed off.

In your experience and expert opinion what is my best path here guys? Is it worth just insisting Dyno to get a refund and go for another brand/model (I’m assuming that is an option)? If so which one?

Thanks!

P.S. Dyno guys have checked the pressures, i.e. reduced the mains down to 3bar, and on Gledhill’s telephone advice reduced EV from 3bar to 2.8bar.
 
Can you turn off the coil heating or turn down the cylinder stat to shut the motorized valve and see if it still makes the same noises while using the hot water.

What are the cylinder and EV capacities?.
 
Can you turn off the coil heating or turn down the cylinder stat to shut the motorized valve and see if it still makes the same noises while using the hot water.

What are the cylinder and EV capacities?.
Hi, it still makes a popping noise when both valves are shut and hot water is used. Cylinder is 210l and EV is 19l (Zilmet)
 
Seems normal enough, the pressure will rise to 4.1bar when heating from cold but will fall to 3bar once 4 or 5 litres of HW is drawn off, so if the PRV is working properly then the cylinder pressure should stay very steady with a very small fall off if large volumes of HW are being drawn off which would suggest no real reason for flexing due to fluctuating cylinder pressures. Unlikely to be EV. Can you see any fluctuations in the pressure (if PG fitted)?.
Maybe suggest to G3/Dyno that the precharge pressure is reduced to 2 bar which would ensure that the diaphragm isn't bottoming out if cylinder pressure fell to 2.8 bar under heavy draw off, it would result in a cylinder pressure 4.5bar on initial heating but again will fall to 3bar once a few litres of HW drawn off.
 
Sounds like the insulation maybe at fault
 
Any pictures of the cylinder and how it has been installed ?? I recently had to fit a pressure reducing valve on a unvented cylinder this should of been fitted as part of the packaged controls but wasn't for some reason ? pressure would build up within the cylinder over night then when hot water was drawn off in the morning the out going pressure was released and caused all sorts of pops and bangs , check your cylinder is well supported over it entire base , and the pipework is well supported also . Kop
 
Samba1 said that Dyno reduced the mains pressure down to 3bar so assumed that a PRV was installed, throttling useless as pressure will build up with no usage, unless PRV is drop tight then same result.
 
Any pictures of the cylinder and how it has been installed ?? I recently had to fit a pressure reducing valve on a unvented cylinder this should of been fitted as part of the packaged controls but wasn't for some reason ? pressure would build up within the cylinder over night then when hot water was drawn off in the morning the out going pressure was released and caused all sorts of pops and bangs , check your cylinder is well supported over it entire base , and the pipework is well supported also . Kop
Thanks @Kop, A reliance water controls combination valve has been fitted (it came with the cylinder along with a 19l zilmet EV), and the mains (as fault eliminating effort) has been fitted with a PRV, set to 3bar, and EV reduced to 2.8bar on Gledhill’s technical advice, but this morning as hot water was being drawn (and cold being fed into cylinder), I heard 2 or 3 loads pops within a space of ~45mins, if my assessment is not wrong, it’s usually within a few seconds of hot water being drawn.

I have posted pictures taken during install, as that shows pipe work.

The entire base is not actually supported, the old cylinder base was used. Not sure you can make out, but the cylinder has a crease about 8 to 10 inches long on the left hand side wall. This is how it was supplied. It did concern me a little but I suspected that it’s cosmetic, but if these cylinders have a thin internal wall, perhaps it has deformed and that is moving in and out as pressure changes?
 

Attachments

  • 5DEDAF39-2F51-4C69-9BCD-4DC2966D2D1A.jpeg
    5DEDAF39-2F51-4C69-9BCD-4DC2966D2D1A.jpeg
    292.5 KB · Views: 38
  • 1FE356E4-F27B-4B3E-B414-6BDA334A45F4.jpeg
    1FE356E4-F27B-4B3E-B414-6BDA334A45F4.jpeg
    241.7 KB · Views: 41
  • 7C1E3C20-872F-421C-9C24-E606704EF057.jpeg
    7C1E3C20-872F-421C-9C24-E606704EF057.jpeg
    295.9 KB · Views: 35
  • 11FF7BAE-AE26-46A0-A28C-2929865E9C5C.jpeg
    11FF7BAE-AE26-46A0-A28C-2929865E9C5C.jpeg
    276.1 KB · Views: 37
  • 7A847557-7AA5-4926-AAFD-8078186CD990.jpeg
    7A847557-7AA5-4926-AAFD-8078186CD990.jpeg
    259.3 KB · Views: 37
Samba1 said that Dyno reduced the mains pressure down to 3bar so assumed that a PRV was installed, throttling useless as pressure will build up with no usage, unless PRV is drop tight then same result.
Hi @John.g, sorry for being a little thick here, I’m not quite following part of your post “throttling useless as pressure will build up with no usage, unless PRV is drop tight then same result.”, Am I correctly understanding it that reducing cold feed to house was not needed? Dyno did that as 1 shower started to run luke warm, and in the other shower it started to run stone cold, so it was done to balance the cold and hot to mixer showers, however it hasn’t helped though, they say nrv and/or thermostat in mixer showers now at fault (and they don’t cover that) but previous cylinder gave no issues with showers, (I now have a number of significant plumbing issues which all started as part of diagnosing air getting into rads issue, which still remains unresolved, and new additional issues manifesting). Not to confuse matters I posted the original issue with my rads building up with air as a separate thread, but oddly my cylinder was replaced by Dyno as part of a fault elimination step, and now rads still building up with air and new cylinder has presented alarming issues, and to top it off, since cylinder replaced the showers are running cold. I suspect the lack of flushing of cylinder installation may have caused debris to travel to mixer valves and causing the (Triton Combi HP) thermostatic mixer showers to become defective, only logical explanation I can come up with.
 
If dyno reduced mains feed pressure to house by just throttling the stopcock then yes that will cause problems when mixing hot and cold water as the throttled pressure will vary from full mains pressure to low pressure which is trying to mix with HW at a now fixed pressure of ~ 3bar, if all the cold water pressure is reduced (with a PRV) then it should work reasonably well but the normal way is as shown in the attached, don't know if yours is like this or not.
Also the EV is better off on the cold water side (as shown) as it act as a shock absorber.

Edit: This is a Glendhill schematic so might assume that dyno modified it like below??.

1640520246208.png
 
Last edited:
If dyno reduced mains feed pressure to house by just throttling the stopcock then yes that will cause problems when mixing hot and cold water as the throttled pressure will vary from full mains pressure to low pressure which is trying to mix with HW at a now fixed pressure of ~ 3bar, if all the cold water pressure is reduced (with a PRV) then it should work reasonably well but the normal way is as shown in the attached, don't know if yours is like this or not.
Also the EV is better off on the cold water side (as shown) as it act as a shock absorber.

Edit: This is a Glendhill schematic so might assume that dyno modified it like below??.

View attachment 67532
Dyno fitted a PRV under kitchen sink to reduce the cold mains to 3bar. The cylinder came with a combination valve, (also called mono block valve I think?) so it’s a NRV, PRV and ERV all in one, and the cold supply then splits to EV and cylinder.

I’ve attached a couple of pictures to try to show the actual configuration.
 

Attachments

  • 4D9BBDE0-8D94-42A4-BF9B-649A5AF19196.jpeg
    4D9BBDE0-8D94-42A4-BF9B-649A5AF19196.jpeg
    228.3 KB · Views: 22
  • E2878EB4-576A-4497-B899-5C55E92456C4.jpeg
    E2878EB4-576A-4497-B899-5C55E92456C4.jpeg
    357.1 KB · Views: 23
Regarding cylinder, do you have full mains pressure then the PRV, then the balanced cold water to mixer taps, shower etc, then the ERV, the EV should also be taken off here. What indication do you have of the pressure? is there a PG fitted somewhere?. What has the under sink PRV to got do with this, if anything?., is it just supplying mains cold water at reduced pressure (via a PRV) to single (non mixing) tap or taps?.
 
Regarding cylinder, do you have full mains pressure then the PRV, then the balanced cold water to mixer taps, shower etc, then the ERV, the EV should also be taken off here. What indication do you have of the pressure? is there a PG fitted somewhere?. What has the under sink PRV to got do with this, if anything?., is it just supplying mains cold water at reduced pressure (via a PRV) to single (non mixing) tap or taps?.
Yes that’s right. The under sink PRV with PG was Dyno’s effort to help balance the cold and hot supplies to thermostatic mixer showers, ie to get 3bar on both hot and cold. Hasn’t helped though, shower goes hot and cold as other taps around the house are used, I suspect debris from the cylinder install has made its way to them and the NRV and/or thermostatic valves are now playing up. The single non-mixer hot taps are absolutely fine, so I’m guessing the mixer shower valves (Triton Combi HP) are now need replacement? At £150 a piece for the thermostatic valve I’ve been asking in these forums whether it’s better to replace like for like valve (stock is still available) or get a newer mixer shower, but that means more plumbing work which I’m hesitant given the loud cylinder popping issues going on, (and Dyno indicated that they don’t cover showers, even though the shower saga started immediately after the cylinder was installed). One thing to note is that the old cylinder was 3.5bar version (Premier Tribune), whereas the Gledhill StainlessLite is 3bar supplying 2 en-suite and 1 bathroom.
 
Last edited:
How do you know what pressure the cylinder and balanced cold water are set to?
To be honest I don’t. The gauge on the cold mains under sink says 3bar, and the combination valve supplied with the cylinder is fixed to 3bar in the airing cupboard, that said Dyno have not measured the pressure at the cylinder. Forgive my ignorance here, but the cold feed to showers are fed directly from the mains, as are all other cold taps. They’re not fed off the combination valve, as that was the original set up with the old cylinder. So if I have understood this correctly, I do not have a balanced cold feed to showers, but instead relying on the PRV under sink to offer 3bar to cold supply into thermostatic mixer showers.
 
If I understand you correctly, it looks that way, so what is the balanced cold supplying, if anything? just to be clear, whichever PRV is supplying the cold feed to the mixer valves should also be supplying the cold water supply to the HW cylinder, ideally all supplied from the valve block, like below. If you can install a PG on the HW cylinder and set the PRV to give exactly the same pressure as the other PRV is giving (3bar) then the mixers may work OK but far better to do it as schematics show. The PRV sometimes has a blanked PG connection.

Can you post a close up photo of the valve block components.

1640532175424.png
 
If I understand you correctly, it looks that way, so what is the balanced cold supplying, if anything? just to be clear, whichever PRV is supplying the cold feed to the mixer valves should also be supplying the cold water supply to the HW cylinder, ideally all supplied from the valve block, like below. If you can install a PG on the HW cylinder and set the PRV to give exactly the same pressure as the other PRV is giving (3bar) then the mixers may work OK but far better to do it as schematics show. The PRV sometimes has a blanked PG connection.

Can you post a close up photo of the valve block components.

View attachment 67542
You’ve got it spot on, there is no balance cold supply from the valve block it is blanked, as the cold supply pipework to showers is not exposed in any way from the airing cupboard and so remains fed directly from the mains (which has the 3bar PRV and gauge). I’ve attached a video perhaps that might make it easier to see setup.

I will ask if Dyno will put a PG on the cylinder, good suggestion!
 

Attachments

  • image.jpg
    image.jpg
    292.8 KB · Views: 18
  • image.jpg
    image.jpg
    296.1 KB · Views: 18
Last edited:
They’ve fitted a pressure reducing valve under the sink so no need to take a balanced cold supply off
 
But what is the HW cylinder pressure if not fed from this PRV.,??

It will be as there both feed in series from the mains stop tap
 
You’ve got it spot on, there is no balance cold supply from the valve block it is blanked, as the cold supply pipework to showers is not exposed in any way from the airing cupboard and so remains fed directly from the mains (which has the 3bar PRV and gauge). I’ve attached a video perhaps that might make it easier to see setup.

I will ask if Dyno will put a PG on the cylinder, good suggestion!
View attachment 67544

Can you clarify for me your understanding of these water supplies.

Is it mains, then PRV (reduced to 3bar) then this supply to mixer taps/shower.
AND Mains to cylinder block PRV then this supply (3bar) to HW cylinder.
or is it
Is it mains, then PRV (reduced to 3bar) then this supply to mixer taps/shower.
AND outlet (3bar) from the above also supply to HW cylinder but through the cylinder block PRV.

Where is the cylinder cold water supply NRV installed?
 
Last edited:
Can you clarify for me your understanding of these water supplies.

Is it mains, then PRV (reduced to 3bar) then this supply to mixer taps/shower.
AND Mains to cylinder block PRV then this supply (3bar) to HW cylinder.
or is it
Is it mains, then PRV (reduced to 3bar) then this supply to mixer taps/shower.
AND outlet (3bar) from the above also supply to HW cylinder but through the cylinder block PRV.

Where is the cylinder cold water supply NRV installed?
Yes, it’s the former set up.

I’ve tried to draw out the setup, hope that makes some sense. I believe the cylinder cold water supply NRV is within the combination valve, which precedes the EV and Cylinder.

EV was reduced to 2.8bar by Dyno on Gledhill’s telephone support, but still hear popping alarmingly when water is being drawn. I really suspect the cylinder is flexing in and out, just like a plastic water bottle when pressure changes. The stainless LITE cylinder is lightweight perhaps due to thin internal cylinder wall? This 210litre cylinder weighs 33kg, other 210litre ones I see weigh 45kg… just a thought…
 

Attachments

  • B4DCBF48-2406-44F5-BE2C-1AC05A591F68.jpeg
    B4DCBF48-2406-44F5-BE2C-1AC05A591F68.jpeg
    131.2 KB · Views: 38
Monitor the pressure gauge at the prv when a shower and cold tap are running and see what pressure you have ? You may have 3 bar standing pressure but not 3 bar at full flow ?
 
Ideally yes but its a new install so the combination set up should be factory set ? you need to make sure your putting 3 bar water pressure and at a decent volume 20 + litres a minute into the cylinder, if you take more out than you put in it can cause the problem your experiencing.
 
Hot and cold supplies ideally how it should be installed 😉
 

Attachments

  • Screenshot_20211227-210943.png
    Screenshot_20211227-210943.png
    499.4 KB · Views: 24
Video watched, one thing I can see wrong supply taken from cold water prv not from inlet combination valve.
 
Last edited:
The point was made that if both PRVs are supplying water at the same pressure then system should work OK, I would think that you could have at least 0.5bar difference in the two and still have proper mixing but I would agree though and can't really understand why it wasn't done the "proper" way, I Iinclude a schematic once again which is quite clear, the EV is also wrongly installed so all these might conspire to cause noise in a paper thin unvented cylinder.

1640644195967.png
 
The point was made that if both PRVs are supplying water at the same pressure then system should work OK, I would think that you could have at least 0.5bar difference in the two and still have proper mixing but I would agree though and can't really understand why it wasn't done the "proper" way, I Iinclude a schematic once again which is quite clear, the EV is also wrongly installed so all these might conspire to cause noise in a paper thin unvented cylinder.

View attachment 67600
Thanks John.G I did question Dyno if the EV should be installed in the way it was, they said no. However, I was merely asking about the way it was piped, I.e. the flow of cold water has to make a 90 turn to go into the cylinder. Is this what you are indicating by being wrongly installed, or is it that it should be connected directly to the combination valve? I’m not 100% sure what ought to be the correct way…
 
I wouldn't be overly worried about a 90deg turn but I would much prefer to see a balanced cold mixing with the hot, a balanced cold means coming off the same PRV as the cold supply to the cylinder, ie the combination valve block. or whatever its called.
"I did question Dyno if the EV should be installed in the way it was, they said no." why didn't they change it then?.
 
I wouldn't be overly worried about a 90deg turn but I would much prefer to see a balanced cold mixing with the hot, a balanced cold means coming off the same PRV as the cold supply to the cylinder, ie the combination valve block. or whatever its called.
"I did question Dyno if the EV should be installed in the way it was, they said no." why didn't they change it then?.
Sorry, my typing is terrible!!!

Should read:

"I did question Dyno if the EV should be installed in the way it was, is it wrong? they said no that’s not a problem”
 
Well, if glendhill's installation is like the one I've posted there is no way that they will provide a new cylinder. They must have sold hundreds of these Stainless Lite, they can't all be noisy?.
A quick look through the installation manual doesn't show the position of the EV but it certainly shows the cold feeds taken off the combination valve.
 

Attachments

  • StainlessLite-Manual-Issue.pdf
    1.5 MB · Views: 10