Recent content by GQuigley67

  1. GQuigley67

    Unvented cylinder reduced flow rate

    Client noticed the magnesium aneode before me, he remember what it was for from his chemistry days... I was clueless oops! Then again he is a senior A&E doctor in local hospital so he's no dummy haha.
  2. GQuigley67

    Unvented cylinder reduced flow rate

    Just an update folks... Turns out that it's a cylinder made of ferrous metal, it had a magnaseum anedode in it which was meant to be checked every year, cylinder has never been serviced, so it is full of sludge!! Replacing cylinder in near future Never came across a cylinder like that...
  3. GQuigley67

    Unvented cylinder reduced flow rate

    Double check valve is after stopcock so can't be it as balanced cold is ok, will let you know how I get on.
  4. GQuigley67

    Unvented cylinder reduced flow rate

    alL hot outlets, balanced cold ok. Can only think tank connection at cold feed, possibly rust deposits from the old combination valve?(valve was rusty as hell its old and bulky) my first diagnosis of filter was wrong so don't want to start draining tank etc to find out I'm wrong again
  5. GQuigley67

    Unvented cylinder reduced flow rate

    When you first open a tap pressure and flow rate is good, it then dies down like a combi would reducing from approx 20 l/min to about 10 l/m. Balanced cold doesn't have this issue, expansion vessel replaced due to being burst, couldn't clean filter in combination valve so temporary bypassed it...
  6. GQuigley67

    Gravity to sealed question

    If their cheap then I'll just go to BSS and buy one, least they can assist with what adapators I need. Would hate to order online and it wasn't BS
  7. GQuigley67

    Gravity to sealed question

    It was a Worcester one, last year probably around 400-500, was from plumb center though and probably didn't have terms on commercial.
  8. GQuigley67

    Gravity to sealed question

    Glad to hear, was expecting Combi PHE prices lol. Last 80kw one I got was crazy money
  9. GQuigley67

    Gravity to sealed question

    The boiler needs to be open vented, I need to change the heating to sealed so seperarion with a PHE is required. Kinda messed up on my design and was in sealed system auto pilot mode not realising it was an open vented thermal store, so system has major air issues now, hoping it's not gonna be...
  10. GQuigley67

    Gravity to sealed question

    got an open vented electric thermal store I want to convert the heating system to a sealed system due to pipework being above the F&E. boiler is in airing cupboard and pipes drop from loft to rads, the boiler is 9kw so I need a plate heat exchanger, was wondering if taking one from a Combi would...
  11. GQuigley67

    Trying to contact Barry Boud (Plumbers) ltd

    You have a leak on installation pipework after 3 years?? Not a chance anyone will be returning to fix that for free
  12. GQuigley67

    To bung or drain down?

    Be mindful to keep only one open end as you change the valve, or swap really quick if possible.
  13. GQuigley67

    Fed up With this ...

    I can earn £225 as part of a 2 man one a day heating team, work bum off for it though, knocked contract back in January because I was flat out busy !
  14. GQuigley67

    Fed up With this ...

    Classed as a total loss for this !!! I'm disputing it though
  15. IMG_0403.JPG

    IMG_0403.JPG

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock