hello,

I have a Worcester greenstart 440 Cdi combi boiler feeding a wet underfloor to my whole house. There’s one manifold upstairs and onedownstairs.

The underfloor manifolds have a trv to make sure the flow temperature remains at 40-50 (or even lessbecause I have a laminate floor).

I have nest thermostats in everyroom with a temperature probe forcut off to protect the floor etc so it’sall done properly.

One of the seals went near one of thetrv, So I changed that only to find it’scrusted up the trv itself. I can order a new one but in the mean time I justset the combi boiler flow to 45 C and removed the TRV so my heating stillruns.

I don’t have any radiators, and the combi feeds only the underfloor systems. I know the combi heating flow temperature usually needs to be around 70 C for it to condense and save energy when the exhaust hits 55-56 C, but is that more efficient than just running the boiler at 45 Cand removing the TRVs?

I read about low heat energy systems but I’m not entirely sure if a combi is very efficient at 45 C since doesn’t it heat exchange to save energy heating the tap water too? If the tap water ishotter than 45 C it will end up heating the pipe directly all of the time?

I’d be interested in your opinions onthis. Running the combi at 45 C is simpler and less prone to error, but is it efficient?
 
you will damage the boiler if you run that set up for a long time return needs to be above 50-55 dc
 


I just read that the lower the return temperature the more efficiently the boiler runs. This seems ad odds with other advice - although that seems to be tartgeted at radiators which they estimate will drop 20C (from 70 to 50) with TRV's fitted.

Very confused now. I also sent an email to Worchester.
 
Well too high.
Flow temp should not be so high, normally it should be set tbetween 55-60 max. The ideal figure would be 15dc between flow and return but in real life you will have a 10 Kelvin difference.
 
I just read that the lower the return temperature the more efficiently the boiler runs. This seems ad odds with other advice - although that seems to be tartgeted at radiators which they estimate will drop 20C (from 70 to 50) with TRV's fitted.

Very confused now. I also sent an email to Worchester.
That’s quite right, the lower it is the more efficient it runs. Due to the fact that the return will be preheated from the fumes and therefore you will reduce the amount of gas usage
 
That’s quite right, the lower it is the more efficient it runs. Due to the fact that the return will be preheated from the fumes and therefore you will reduce the amount of gas usage

totally wrong

you run that set up and you boiler will only last a couple of years hex will internally scale up due to to low of a return temp

the lowest i would set the flow temp is 60 (45-50 return temp)
 
totally wrong

you run that set up and you boiler will only last a couple of years hex will internally scale up due to to low of a return temp

the lowest i would set the flow temp is 60 (45-50 return temp)
Really, i am so wrong :)
Don’t think so. The hex will scale up anyway in England, doesn’t matter how you set the temp on the boiler ...

It’s a condensing boiler and it’s designed to run on low flow temp. Let’s say you set the flow temp on 55dc return will be about 45 that’s a difference of 10 Kelvin. The flue gases will have about 55dc that will be hotter than the return temp and therefore gives it energy further and reduces the amount of gas usage. What’s the point of setting it on 65/70dc flow temp and return will be about 55/60 you will not use the heat from flue gases at all and that’s called wastage or inefficient. The reason for this is that condensing boilers also extract / take , energy from the hot flue gases. They cool it with the return water, condensing moisture contained. For this to work properly, the temperatures in the flow and return should be low.

Scale won’t be removed due the heat :) check your kettle
 
Thanks for you replies.

Just for some added info we have very hard water here so I have a hefty water softener and a hefty filter after it to remove chlorine and salt. Those feed the entire house.

Yes I know softened water shouldn’t go into a boiler usually but the second filter takes care of any salt etc. I have tested the water output.

So given the above, and also that at 50 - 55C into the underfloor the return is 40-45 C what should I do:

1) set boiler flow to 70C, and set TRV at underfloor manifold to 50C / or give me different values.

Or

2) set boiler at 50 C and remove the TRVs / or give me a different value.

FYI the underfloor optimum temperature is 40-55 C (because it’s laminate wood lower is better as it doesn’t trigger the cut off)
 
Really, i am so wrong :)
Don’t think so. The hex will scale up anyway in England, doesn’t matter how you set the temp on the boiler .

It’s a condensing boiler and it’s designed to run on low flow temp. Let’s say you set the flow temp on 55dc return will be about 45 that’s a difference of 10 Kelvin. The flue gases will have about 55dc that will be hotter than the return temp and therefore gives it energy further and reduces the amount of gas usage. What’s the point of setting it on 65/70dc flow temp and return will be about 55/60 you will not use the heat from flue gases at all and that’s called wastage or inefficient. The reason for this is that condensing boilers also extract / take , energy from the hot flue gases. They cool it with the return water, condensing moisture contained. For this to work properly, the temperatures in the flow and return should be low.

Scale won’t be removed due the heat :) check your kettle

:D wrong hex for a start your thinking of the domestic hot water plate heat exchanger Lol

Also you haven't taken in for heat loss through the pipes
 
Thanks for you replies.

Just for some added info we have very hard water here so I have a hefty water softener and a hefty filter after it to remove chlorine and salt. Those feed the entire house.

Yes I know softened water shouldn’t go into a boiler usually but the second filter takes care of any salt etc. I have tested the water output.

So given the above, and also that at 50 - 55C into the underfloor the return is 40-45 C what should I do:

1) set boiler flow to 70C, and set TRV at underfloor manifold to 50C / or give me different values.

Or

2) set boiler at 50 C and remove the TRVs / or give me a different value.

FYI the underfloor optimum temperature is 40-55 C (because it’s laminate wood lower is better as it doesn’t trigger the cut off)

Leave the trvs in place / replace them if there leaking and set to manufacturer spec for the floor type

I would set it to 60 (flow ) and set it up correctly

Eg balancing your loops so you get the correct difference Yout looking around 40-45dc for your return temp
 
Last edited:
:D wrong hex for a start your thinking of the domestic hot water plate heat exchanger Lorl

Also you haven't taken in for heat loss through the pipes
really ? I’m wrong ... that’s fine with me :) i will keep doing it the way I got taught. Keep setting boiler temp to 70dc it’s fine with me too but the heating costs will speak for itself
 
Hi kam,what temperatures you after? For me underfloor heating and central heating are total wo different things if you like. As you know the ufh will ne

really ? I’m wrong . that’s fine with me :) i will keep doing it the way I got taught. Keep setting boiler temp to 70dc it’s fine with me too but the heating costs will speak for itself

What temp does most boilers start condensing ?

55 is the answer so with a 15dc difference you will condense and with the new boiler plus kit you will save more etc

Also have you check the boiler out, it has a heat store so that heats your hot water as well
 
What temp does most boilers start condensing ?

55 is the answer so with a 15dc difference you will condense and with the new boiler plus kit you will save more etc
England is 20 years behind mate to start with.
As I said if you set 55 the return will be about 10kelvin different so it will use the flue gas as energy instead of wasting.

Boiler plus is for 20 years in Germany .. we only install boilers with integrated heat recovery units , weather compensation sensors etc. However, Like Atag says, they are apparently Europe’s best boiler which is wrong market leader is and will be Vaillant .. the guy from Atag is a kitchen company by the way he just started 10 years ago to do some boilers .. :) Lol
 
England is 20 years behind mate to start with.
As I said if you set 55 the return will be about 10kelvin different so it will use the flue gas as energy instead of wasting.

Boiler plus is for 20 years in Germany .. we only install boilers with integrated heat recovery units , weather compensation sensors etc. However, Like Atag says, they are apparently Europe’s best boiler which is wrong market leader is and will be Vaillant .. the guy from Atag is a kitchen company by the way he just started 10 years ago to do some boilers .. :) Lol

If sized correctly I would want more of a difference more like 15-20dc
 
If sized correctly I would want more of a difference more like 15-20dc
As said in my previous post ideally you want 15dc ( that’s the ideal figure ) between flow and return. But it’s totally silly to run the flow temperature via 70dc ... the lower it is the more efficient it runs. And due to the passive heat recovery units and weather compensation you will gain even more on savings. But if you think you are right that’s good with me I’ll stick to the 55dc. Why disagreement? Due to the fact I know that Atag isn’t market leader or because England is 20 years behind ?
 
Erm I see you guys seem to have got into a debate over this!

So if I only want 40-50C for the floor what do you recommend I run the boiler flow at if not 70C

I understand you both have different views but I’d like to hear the lower temperature recommendation too.

Why would I run it at 60 C If I only need 40-50? Id be happy to run the underfloor at 45
 
60-65

Also running at a lower temp would alter your hot water performance eg longer time to wait for hot water etc
 
Worchester replied and said it's fine to run it at 50C, and also it won't affect the hot water.

I'm waiting for the TLV's and i'll do some tests both ways.
 
Status
Not open for further replies.

Reply to Combi boiler flow temperature with underfloor heating in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock