2
Hi guys and girls.

So…. Bought an apartment in a conversion rather than new build. Since buying it I’ve been experiencing headaches, sickness and dizziness. At the time I just thought I was coming down with something but then a TV engineer came to install an aerial in the loft and he showed me two pipes that aren’t even connected and these are the boiler flue. It doesn’t even look like they’ve ever been connected and they just won’t fit do you their locations. The engineer said to turn the boiler off immediately and contact gas safe which I’ve done. He said my headaches etc could be as a result of carbon monoxide going into the loft and slowly into my apartment through 3 loft hatches.

Gas safe as due to come out and have invited to engineer who signed off the installation to attend also. He’s called the developer who he worked on behalf on when the building was converted and they are saying that there is nothing wrong with the installation and telling me to cancel gas safe and just let their guy come out who is the same guy who signed it off.

Please can you review the attached photo and confirm that this is not installed correctly and that the boiler flue should be connected to outside so all fumes go out rather than into the loft space?
25E7A37F-8F21-48A7-96CB-449BC9E80EA1.jpeg
 
Also don’t let the engineer attend without gas safe there eg before they come
 
Have you been check out medically ?
 
Is that corrogated asbestos roofing sheet that the flue has been punched through? The photo isn't the clearest but I think I can see some sort of fibres.

Make sure the installer isn't allowed access before Gas Safe has inspected. They could be looking at criminal charges so will want to cover their tracks.

Looks to me as through the section going through the roof was not properly supported and restrained, got bent sideways and popped out of the lower section.
 
Is that corrogated asbestos roofing sheet that the flue has been punched through? The photo isn't the clearest but I think I can see some sort of fibres.

Looks to me as through the section going through the roof was not properly supported and restrained, got bent sideways and popped out of the lower section.

That's galvanised box corrogated steel decking / roofing, not asbestos, similar to the pic below.
It'll have insulation then probably a high performance Butyl membrane on top or cheapskate hot felt.

Looks like there's condensation under the roof sheet from P.O.C.s.

Looks like the flue was complete at one point with it having a mark to show depth and what looks like the shadow of where the seal was just below.
It may be that the roofer pulled the flue up when sealing the flashing around it, or maybe someone else has tried to lift it out.
If it had a bracket at the joint at least the flue wouldn't have fallen to the side.

roof deck sheet.PNG
 

Reply to Is my flue installed incorrectly? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
338
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
191
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock