With all this talk about potentially switching from gas to hydrogen or even blending some hydrogen into the gas, does anyone know how this affects the dew point of the products of combustion? With natural gas I think it starts to condense around 57C or so, so the return temperature needs to be under that to get significant condensing in a modern boiler. If the gas was blended with say 10% hydrogen, does it change that temperature? Actually it would be nice to see a chart going from 0% 10%, 20% ... 100% hydrogen. Has anyone seen such a chart?
 
Will be the same as natural gas or winthin a degree of two
 
Mains gas is CH4, 1 part carbon and 4 parts hydrogen. The higher the hydrogen content within a fuel the more water vapour is produced as a by product. This in turn leads to a higher partial pressure of water vapour in the medium (this case the flue gases) which increases its dew point temperature.
Mains gas is as you say starts to condense at about 57°c and condenses considerably more the lower the return temperature can be. Oil on the other hand has less hydrogen in it and as a result requires a temperature closer to 47°c to start condensing.
 
What I was astonished to read was that the CO2 emissions saving was less than 10% running a gas blend which is better than nothing but still, hardly planet saving considering the push. Yet modern building and existing insulation standards are relatively Sod poor.
 
So although it may only change a small amount, it will be in the right direction as far as condensation is concerned, as the more hydrogen there is, the higher the return temperature can be, which is good.

Still would be nice to see a table, that gives the temperature for various blends up to pure hydrogen. I can't seem to find one.
 
You probably never will!

As far as I am concerned, the only thing that is going to make major changes to the state of the environment is Government Legislation.

Governments will not make Legislation's that will impact all its Citizens financially to a substantial amount.

Imagine a Government that declares we are going to Greener Energy.
It will only amount to an extra 20% across all your energy bills, including vehicle registration and fuel prices.

I live in Melbourne.
The amount of money you pay for a solar hot water system will take about 8 years to recoup, over having a non solar system installed.
Where the benefit in that?
 
I live in Melbourne.
The amount of money you pay for a solar hot water system will take about 8 years to recoup, over having a non solar system installed.
Where the benefit in that?
With today's interest rates, 8 years is not bad, really, so may be worth it, in Melbourne. The solar installation also makes your boiler last longer and should itself last some considerable time. Of course, if the hot water system becomes a status symbol, then the cost is irrelevant. After all, how long does double-glazing really take to pay for itself vs draughtproofing existing single-glazed windows in the UK, and how many houses still have single-glazing?

It seems the costs of mitigation of climate change will be much lower than the adaptation costs. It has been suggested that people who can afford it will accept extra costs happily enough. The problem is that systemic change is required and it has been suggested that people will accept cost, provided they don't have to change their lifestyle - which would be required if we are to ditch the current relentless pursuit of continuous economic growth.

The trouble is, the powers that be have an interest in the current economic system and they do a very good job of influencing mainstream thought. Governments will tend to lag behind ideas whose time has come.
 
Has anyone seen such a chart?
Here's a quick calculation that assumes 10% excess air and uses the Antoine formula to calculate SVP for water as a function of temperature.

1618707948171.png
 
Wow, that is a lot by the time you get to pure hydrogen, around 25C. This means that boiler running on pure hydrogen will not really need over sized rads to be condensing most of the time.
 
Wow, that is a lot by the time you get to pure hydrogen, around 25C. This means that boiler running on pure hydrogen will not really need over sized rads to be condensing most of the time.
I think you must mean 15°C. Keep in mind that if the return temperature is at the dew point the amount of condensation will be negligible. It needs to be significantly lower to actually have a significant impact.

For example, at a dew point of 57°C the partial pressure of H2O in the combustion products will be 131 mmHg. A return temperature of 45°C will reduce the H2O SVP to 72 mmHg, which means that only about 45% of the H2O will be condensed.

According to my calculation, a boiler that runs on pure H2 with lambda = 1.1 will have a pp(H2O) = 240 mmHg. A return temperature of 55°C, which corresponds to SVP of 118 mmHg, will allow 50% of the H2O to condense.
 
I think you must mean 15°C. Keep in mind that if the return temperature is at the dew point the amount of condensation will be negligible. It needs to be significantly lower to actually have a significant impact.

For example, at a dew point of 57°C the partial pressure of H2O in the combustion products will be 131 mmHg. A return temperature of 45°C will reduce the H2O SVP to 72 mmHg, which means that only about 45% of the H20 will be condensed.

According to my calculation, a boiler that runs on pure H2 with lambda = 1.1 will have a pp(H2O) = 240 mmHg. A return temperature of 55°C, which corresponds to SVP of 118 mmHg, will allow 50% of the H2O to condense.

I'm liking your maths and clearly clarifies what I said above in my comment.
 
Haha, yes, 15C.
 

Reply to Dew point of gas-hydrogen blends in the Renewables area at PlumbersForums.net

Similar plumbing topics

Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
200
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
196
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
289
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock