We recently installed a new Gloworm combi boiler in a property and we had a call from the customer to say that when he runs the hot water it comes out a milky colour and feels slimy. Also when he runs the cold tap the boiler fires up and then goes off. This is happening at every outlet. Even when the the washing machine pulls cold water in.

I've been there to check things and can confirm what he has reported.

My question is that has anyone else ever come across this and if so what id the cause / solution.

Oh and Gloworm have been out but not helpful at all. Just basically did what i did when i visited
 
Have you fitted a shock arrestor?
Did you convert from an OV system?
Haven't fitted an arrester yet no but was thinking about that to stop the boiler trying to fire when the cold is turned on but more worried about the milky hot water to be honest

Yes was converted from open vent to combi
 
Last edited:
We recently installed a new Gloworm combi boiler in a property and we had a call from the customer to say that when he runs the hot water it comes out a milky colour and feels slimy.
A milky appearance is normally microscopic air bubbles. If so, if he leaves a sample of the water for a few minutes it will gradually clear as the bubbles rise to the top.

This happens because gases are more soluble in cold water than in warm water so the heating action causes the dissolved air to come out of solution and form tiny bubbles. The tiny bubbles scatter light, which gives the milky appearance. (Milk looks milky because the suspended droplets of fat scatter light.)

The slimey feel is more unusual. It's just possible that he's actually feeling the 'fizzing' bubbles. It's also possible that seeing the milky appearance is triggering his imagination. Either way, when the bubbles clear the slimey feel will probably go too.

If standing time doesn't clear the milky appearance, you can get a sample of water tested by a lab. Will cost about £30 IIRC and will settle the matter.
 
A milky appearance is normally microscopic air bubbles. If so, if he leaves a sample of the water for a few minutes it will gradually clear as the bubbles rise to the top.

This happens because gases are more soluble in cold water than in warm water so the heating action causes the dissolved air to come out of solution and form tiny bubbles. The tiny bubbles scatter light, which gives the milky appearance. (Milk looks milky because the suspended droplets of fat scatter light.)

The slimey feel is more unusual. It's just possible that he's actually feeling the 'fizzing' bubbles. It's also possible that seeing the milky appearance is triggering his imagination. Either way, when the bubbles clear the slimey feel will probably go too.

If standing time doesn't clear the milky appearance, you can get a sample of water tested by a lab. Will cost about £30 IIRC and will settle the matter.
Yeah thanks Chuck did think that its air bubbles as it clears after a few minutes but trying to explain that to a customer is easier said than done as he never had it before. Thanks for your help anyway mate
 
trying to explain that to a customer is easier said than done as he never had it before.
What type of boiler did he have before? If it wasn't a combi that's the difference. If it was a combi maybe the new one is more powerful so the temperature change is more dramatic.
 
all hot outlets produce the same white milky ?
 
all valves fully open ? have you tried just connecting the outlet of the boiler into a bucket to see if its a supply or outlet issue?
 
all valves fully open ? have you tried just connecting the outlet of the boiler into a bucket to see if its a supply or outlet issue?
i haven't as yet no but the boiler is next to the kitchen sink which is where the hot and cold was connected to so connecting a hose to the outlet probably wont be worth it will it ?

Haven't checked valves as yet but will do
 
We do loads of conversions but never had this before so why with this particular one ?
As long as it clears from the bottom to top and doesn't leave a scum or oily film on the surface it's almost certainly air. If it clears from top to bottom it's particulate matter, maybe dislodged limescale, (which might explain the slimey feel) and should be cleared by flushing.

As well as air naturally dissolved in the incoming supply, other possible sources include: (a) a faulty inline pump somewhere; (b) air trapped somewhere in the pipework, e.g. in a dead-leg that needs to be removed.
 
As long as it clears from the bottom to top and doesn't leave a scum or oily film on the surface it's almost certainly air. If it clears from top to bottom it's particulate matter, maybe dislodged limescale, (which might explain the slimey feel) and should be cleared by flushing.

As well as air naturally dissolved in the incoming supply, other possible sources include: (a) a faulty inline pump somewhere; (b) air trapped somewhere in the pipework, e.g. in a dead-leg that needs to be removed.
Good idea Chuck thanks. will do these tests first to see what I get. The limescale being dislodged sounds a big possibility. Thanks for your advice
 

Reply to Combi boiler producing milky slimy water in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
188
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
207
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
4
Views
192
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
287
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
191
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock