I moved house three weeks ago and now, for the first time, have a combi boiler - it's a WB Greenstar 37CDi.

Among the documents given to me is a Service/Maintenance Certificate dated January 2019 whichsays that the boiler is safe to use. Attached to it is the output from a FGA which gives these figures:

02 - 4.9%
CO2 - 9.1%
COppm - 25
CO/CO2 - 0.0002

Are these numbers what would be expected from a boiler which is nearly 11 years old?

I am also concerned about the suitability of the boiler for heating. I did a quick whole-house type calculation which showed that the heat loss is about 9 kW. I have measured all the radiators and, using online data, worked out that they add up to about 9.5 kW. So far, so good. However the CDi 37 has a minimum output of 9.4 kW, so the boiler will be running in on/off mode all the time. I also doubt if the boiler will ever be condensing.

Should I change the boiler now for one with a much lower minimum output or wait until the boiler dies? Ideally, I would convert to a system boiler and unvented cylinder but there is not enough space for both cylinder and boiler in the airing cupboard. One would have to go in the loft.

I have a dilemma: what should I do??
 
You’ll probably only get in minimum ch output of about 5/6 kw on any combi, it’s all about the turn down ratio.

Unvented in a loft, you’d lose pressure at your taps. Put boiler up there.

9kw is quite low, must be a small house... so a bathroom and a half maybe, if so I’d keep your expenses down and put a decent combi in.
 
combis are sized on hot water demand

if your unsure get it serviced by someone you know (your gas safe engy)
 
9.1 may be slightly low depends on how old the boiler is. But I wouldnt be too concerned as that is more fine tuning.

I would always advise getting the boiler serviced by an engineer you trust as you never know who they got to do the service.

As for ripping it out. Live with it for a bit and see how you get on with it. Give it the winter and then if you are not happy with it then plan to do that next summer.
 
9.1 may be slightly low depends on how old the boiler is. But I wouldnt be too concerned as that is more fine tuning.

I would always advise getting the boiler serviced by an engineer you trust as you never know who they got to do the service.

As for ripping it out. Live with it for a bit and see how you get on with it. Give it the winter and then if you are not happy with it then plan to do that next summer.
Or it could be too high. Dependent on what test was done?
 
combis are sized on hot water demand
Which is why so many combi boilers are oversized for CH.

if your unsure get it serviced by someone you know (your gas safe engy)
That sounds like a good idea as the sevice log in the installation manual says that the last service was done in February 2012, when the boiler was just over three years old. (Service only done to comply with warranty??)
 
Dont worry about it. Values are good, however at 25 co ppm and R.0002 this hasnt been done on max output. But theyre allright. The boiler wont be on/off all the time, because the 9.5kw min output doesnt mean it will only ever fire up on minimum output, thus barely negating losses, no. It can and will go higher. Certainly not constantly cycling.
Keep it running for as long as you can. Buy a spare fan if you come across one for a good price (ebay..).
I have a 16 year old potterton system boiler and a vented cylinder on ground floor flat with tank in loft. Changed the fan on it 5 years ago. Pcb is faulty, it will constantly lock out because it thinks it overheats but resumes operation in a few minutes after, would be problem if combi but its not, didnt even notice until fan died. Its literally so old that the case looks warped and twisted, it fits fine though and doesnt leak. Dodgy gas suppliers would still charge me the same amount if I had a AAAAA++ boiler with 90% less gas usage than current one, so its literally pointless to change it. It will always be repairable, its that simple, until it melts or crumbles away.
 
Dont worry about it. Values are good, however at 25 co ppm and R.0002 this hasnt been done on max output. But theyre allright.
A proper check would require the system to be checked at max and min output.

The boiler wont be on/off all the time, because the 9.5kw min output doesnt mean it will only ever fire up on minimum output, thus barely negating losses, no. It can and will go higher. Certainly not constantly cycling.
That depends on how the boiler behaves after the internal thermostat turns it off. Many boilers, particularly older ones, always start at max output, which causes the temperature to rise rapidly. The boiler modulates down until, hopefully, equilibrium is reached and the boiler runs continuously at a low output. But if the amount of heat required is less than the boiler's minimum output, the water temperature continues to rise, the boiler shut offs, and the cycle restarts.

Even if the boiler restarts at minimum output the same thing will eventually happen, but the on period will be longer as the rate of temperature rise will be slower.
 

Reply to Boiler advice needed in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
250
Hi all Noticed bad smell in my drain out side put my hand down and it unclogged it for now however I checked my sewer drain and after flushing my toilet a good few times nothing is going to the sewer so don't know is there a blockage or what way it works many thanks and advice would be grateful
Replies
3
Views
405
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
203
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
148
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
209
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock