Hi there. I wondered if any of you pro’s have seen a strange fault that I’ve had with my Oil boiler.

Long story short, boiler failed to operate when requested. Not in lockout, had a quick check - I’m an industrial control electrician so handy with a meter - couldn’t find much wrong with photocell, solenoid windings etc so started to check the control box out. On inspection I noticed that one of the soldered connections to the heater coil on the bimetallic strip had become detached. Thus when the boiler got the 240v to fire the ignition sequence wouldn’t start as the bimetallic strip wouldn’t heat up. Awesome I thought, it’s a dodgy box. Shelled out £30 for new and hey presto house is warm, wife is happy.

Fast forward, 4 months and exactly the same fault. Strange, I thought so once again checked everything obvious because now I’m suspecting the boiler is killing the box. Nothing I could find apart from having no oil - doh! It then occurred to me that the original time the fault happened I had low oil! But surely this would just cause a lockout??

Anyway, swapped the box - again - to get up and running and stripped the dodgy box down. I resoldered the connection and it’s back to working order. I decided to have a play with it and see if I could get it to fail and I could, by running it through start cycle after start cycle on the bench (putting 240v on and waiting for lockout resetting the lockout as soon as possible then restarting) I noted how the bimetallic strip was starting to hold some heat and then melt the connection solder. At this point I figured I knew what caused the box to fail but couldn’t explain how the conditions on the bench could be replicated by the boiler.

Fast forward another 7 months and once again box has failed with exactly the same failure mode.

Any thoughts appreciated
 
Burner perhaps has another fault - poor combustion or photocell not seeing flame fully or faulty, etc and causing control box to repeatedly go to ignition start up. Also boiler control stat needs checked in operation in case it is sensitive and cycling.
Probably best to get a decent oil service engineer in and explain to them your findings and also get them to do a full service and analyser set up of burner.
Make sure the boiler is then carefully checked for a period to confirm it isn’t frequently cycling on and off.
Your electrical knowledge is no doubt useful, but best not to tinker with oil boilers unless you know everything about them. To ignore proper combustion servicing is neglect.

What sort of boiler and burner is it?
Is is a combi oil boiler?
What sort of flue has it and does it terminate properly and not into a corner for example. (Flue combustion gases drawn into burners can cause terrible cycling).
 
Last edited:
Hi. Thanks for your advice. Boiler is a Worcester danesmoor. Not sure on the burner. It’s a system boiler.

Agree with what you say about getting an oil guy in. But I have the boiler serviced annually and no one has ever found an issue. When I’ve mentioned this fault I just get a shrug of the shoulders and they tell me that they’ve never seen it before. Perhaps I need a new service guy!

It’s a strange one. I’ll keep my eye on it for short cycling.

Thanks
 
Control boxes will burn out if overused obviously, so very likely it is operating the ignition for some reason very often.
The wiring in the control box base would need checked, if that hadn’t already been done
 
The control box receives 50v from the motor (white wire). If there is a fault on the motor it could be cooking your control boxes. Certainly is an unusual fault. Where are you? Perhaps someone on here could look at it for you. Some of the folk that do servicing are a bit limited in their knowledge.
 
The control box receives 50v from the motor (white wire). If there is a fault on the motor it could be cooking your control boxes. Certainly is an unusual fault. Where are you? Perhaps someone on here could look at it for you. Some of the folk that do servicing are a bit limited in their knowledge.

Satronic control box, - so his Danesmoor must have an Inter burner
 
Check for short cycling. If the control box is constantly stop-starting it will wear out quickly. Check your boiler temp / flow and return and Delta T is correct
 
hi did you ever solve the problem. My neighbour is having same trouble. I managed to re-solder the connection to the bi metal strip. however, the latest is the wire winding round the strip has burnt out and unrepairable. can't find what is causing them to overheat.
Any suggestions
 
Hi there. I wondered if any of you pro’s have seen a strange fault that I’ve had with my Oil boiler.

Long story short, boiler failed to operate when requested. Not in lockout, had a quick check - I’m an industrial control electrician so handy with a meter - couldn’t find much wrong with photocell, solenoid windings etc so started to check the control box out. On inspection I noticed that one of the soldered connections to the heater coil on the bimetallic strip had become detached. Thus when the boiler got the 240v to fire the ignition sequence wouldn’t start as the bimetallic strip wouldn’t heat up. Awesome I thought, it’s a dodgy box. Shelled out £30 for new and hey presto house is warm, wife is happy.

Fast forward, 4 months and exactly the same fault. Strange, I thought so once again checked everything obvious because now I’m suspecting the boiler is killing the box. Nothing I could find apart from having no oil - doh! It then occurred to me that the original time the fault happened I had low oil! But surely this would just cause a lockout??

Anyway, swapped the box - again - to get up and running and stripped the dodgy box down. I resoldered the connection and it’s back to working order. I decided to have a play with it and see if I could get it to fail and I could, by running it through start cycle after start cycle on the bench (putting 240v on and waiting for lockout resetting the lockout as soon as possible then restarting) I noted how the bimetallic strip was starting to hold some heat and then melt the connection solder. At this point I figured I knew what caused the box to fail but couldn’t explain how the conditions on the bench could be replicated by the boiler.

Fast forward another 7 months and once again box has failed with exactly the same failure mode.

Any thoughts appreciated
If you're heating engineer can not find anything obvious wire a new control base.Even if the boiler is short cycling it will take more than several months to burn out any components as those we burners are bomb proof.
 

Reply to Satronic/Honeywell 832.3 keeps failing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi need some advice on this odd story, I had a Bosch boiler installed just over 2 years ago by Governments home energy scheme. The company passed all checks, provided certs etc. The government/Green scheme sends 2 other gas boiler engineers to double and triple check things and One was Bosch...
Replies
11
Views
695
I have a customers trianco burner that starts from cold ok for a few minutes (say 3minutes) then locks out then will not stay on. Boiler had not been serviced in a long time and oil filters were bunged up as was the nozzle. I decided to service it with hopes it was simple starving of fuel from...
Replies
1
Views
606
Hi Oil experts. I had a grant wall boiler with a failed transformer. Carried out a service and pretty sooty nozzle, and baffles build up suggest not cleaned in a while. The bottom baffle on the left corner had completely burnet through. Any Idea on the process on how this occurs and why just...
Replies
5
Views
220
I have a Worcester Bosch Greenstar 15i condenser boiler which is about 13 years old. There is a separate hot water tank. Recently the fan in the boiler has started to stay on all the time. My usual engineer took a look at it and advised me to contact the manufacturer. I then had an engineer from...
Replies
3
Views
168
    • Funny
    • Optimistic
Hi, I've got a ferroli 901 boiler, I initially thought the pcb was at fault so bought a new one and I'm having the same problem ( has been connected correctly), I switch the boiler on, all correct leds light up, pump starts, fan starts, pilot fires up, then it shuts down, all lights go...
Replies
2
Views
599
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock