Hello guys.

Please can you help as at wits end. I've changed out 4 radiators over the last 12 months in my house and the last one being yesterday. I now have a F75 code and a S98 information code on my vaillaint Pro eco tec 28 combi boiler.

I had a GSR installer friend come over and he bled the pump and auto air vent which worked for about half and hour. When the missus went to put heating on via remote control thermostat it went back to F75 mode again!

I've bled all radiators starting bottom to top and there is an cold standing pressure of 1.1bar

Is there anything simple that could be done to alleviate this problem as have no hot water or heating. All other rads were no problem just this one.

Thanks all very much

Martyn
 
Hello guys.

Please can you help as at wits end. I've changed out 4 radiators over the last 12 months in my house and the last one being yesterday. I now have a F75 code and a S98 information code on my vaillaint Pro eco tec 28 combi boiler.

I had a GSR installer friend come over and he bled the pump and auto air vent which worked for about half and hour. When the missus went to put heating on via remote control thermostat it went back to F75 mode again!

I've bled all radiators starting bottom to top and there is an cold standing pressure of 1.1bar

Is there anything simple that could be done to alleviate this problem as have no hot water or heating. All other rads were no problem just this one.

Thanks all very much

Martyn

Try putting the pressure up to 1.5 bar if it works it will get you by for a couple of days but you will need an engineer to sort the underlying issue.
 
Pressurise it to about 1.5-1.8. I found vaillants dont like 1 bar and need that extra bit of pressure to work otherwise you will constantly have problems with f75 no matter how many times you replace the part that causes it.
 
Pressurise it to about 1.5-1.8. I found vaillants dont like 1 bar and need that extra bit of pressure to work otherwise you will constantly have problems with f75 no matter how many times you replace the part that causes it.
Thanks mate, so when the heating kicks in it will raise the bar pressure higher. So do you think that'll be OK on the radiators etc? Once raised to 1.5 bar cold do I need to bleed the rads?
 

Reply to Help! Vaillant boiler not working after changing out a radiator in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
249
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
202
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock