Discuss Aqualisa From Pumped To Unpumped Processor in the Plumbing Jobs | The Job-board area at PlumbersForums.net

DjClubber

Gas Engineer
Messages
50
Can you just convert the Processor from the Fully Pumped over to the Un Pumped Processor if the installation is just at the moment Pumped but being converted to a Combi? Ideally want to keep the Ceiling Fed Kit Below and just be able to change the Processor? Will it Wire in the same and be able to use the Start / Stop below? Please can you let me know ASAP??? TY...

The pic shows the manual with both, the pumped is installed at mo but ideally want to change to unpumped for Combi. . .

aqualisa.jpg
 
I think so have to change the whole unit like you say eg from pumped to mains / high pressure but you can keep everything else I think
 
Thanks, appreciated. Will order unpumped version. . . Thanks for the quick replies. Once again Appreciated. . .

The one in the pic ?
 
How do you do it? Push fit sockets onto the stems, take it to copper and then compress a full bore valve onto the copper or do you attach the valves direct to the plastic stems on the valve.

Over the years, using both the grey & black processors, I've done both. What dictated which was used, was simply ease of pipework access.

The last one was approx 18 mths ago and that was direct onto the plastic stems on the supplies and via a pulled bend on the output.
 
Very bad idea

Well they say you learn something new every day!

25 years plumbing and installing countless versions of these showers I did not know you could not do just switch them over. :oops:
(Although I have never needed to).

That brings another question, why the hell is it there then?
 
Well they say you learn something new every day!

25 years plumbing and installing countless versions of these showers I did not know you could not do just switch them over. :oops:
(Although I have never needed to).

That brings another question, why the hell is it there then?

MRB. Every day is a school day :D

If you look closely you'll see that the label is split into the two types of processor. The RH one is the pumped version & the LH one the HP version.

Truth is it's a little confusing. It's all about Aqualisa saving money to use a common label.
 
Well they say you learn something new every day!

25 years plumbing and installing countless versions of these showers I did not know you could not do just switch them over. :oops:
(Although I have never needed to).

That brings another question, why the hell is it there then?
If you look at the cover of the processors you will see that the pumped and standard versions have different pressure ratings. The pumped are only rated for low pressure where the standard versions are rated for higher pressure. I found out the hard way :oops:.
As Dave said, it's a money saver for aqualisa so they only produce one pcb for both the standard and pumped versions. And probably a money maker as your forced to change the processor if you change your system.
 

Reply to Aqualisa From Pumped To Unpumped Processor in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
147
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
5
Views
107
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
115
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
249
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock