22
Hi,
writing up my last report for my gas portfolio and have come up against something i can't work out whilst doing the gas rate figures!!
Data plate shows Hot water pnw 34kw and qnw 34.7kw (hi)
manual shows gas rate norm level 3.78m3/h minimum 3.4m3/h maximum 3.97m3/h
If i fudge a gas rate level to 3.78m3/h that is equivelant to 40.67kw gross which is 36.64nett.
They don't match up? are the data plate figures nett?
I even called valiant, they were useless............
Reason i am asking is that I don't want to mess up my portfolio by making a mistake! my gas rate came out at 3.42m3/h which is too close in my opinion to the MI docs minimum allowance....
Any ideas?
 
I would be happy with that gas rate you will never get it perfect that’s why they allow you a % up or down
 
Vaillant weren't of much use, only asked CO2 levels from a safety point of view... He said i could email them but they will take ages to reply.. LOL. I just wanted to try and understand the levels in MI's against data plate on the boiler......
Inlet pressure was ok 19.5mb
 
just to be clear, my issue isn't really with my personal gas rate obtained. Its with Vaillants quoted figures!
Ive attached the data plate........ and as stated the norm gas rate is 3.78m3/h +5% -10%
what would you say the max input is from the data plate and is that a nett figure?

IMG_5844.jpg
 
I'm not sure what the issue is? You've gas rated it and it's within the MI range. If the MI allows you that range then it's correct. TBH i've never had a Vaillant over read that much anyway, they're usually slightly under the nom.
 
Ok.....
Install was with official Vaillant installer..... Gas rate obtained by putting boiler into installer modes and running hot water!!
my point as stated..........
vaillant instructions show 3.78m3/h as norm with tolerance of +5%/-10%
boiler data plate (as shown in picture) shows max heat input pnw 34kw and qnw 34.7kw.
gas rate is a formula..... if i work out a gas rate of 3.78m3/h gross this gives you a kw level of 40.67 gross or 36.64nett NOW.... if you look at data plate. that means that the norm expected for this boiler is 34kw or 34.7kw (data plate)
the point i am making is, i don't think the vaillant figures can tally up correctly...
I know my gas rate obtained is within guidelines, i just don't get the manufacturers levels.....
 

Reply to Vaillant eco TECH plus 835 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
187
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock